Thank you - a direct HIT!

SL

From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of Dennis Wilson via Sprinklerforum
Sent: Wednesday, June 24, 2020 2:27 PM
To: sprinklerforum@lists.firesprinkler.org
Cc: Dennis Wilson <dwil...@blackhawksprinklers.com>
Subject: RE: Listed sprinkler guard for horizontal or vertical spray sidewalls

Reliable F1FR-56

From: Sprinklerforum 
<sprinklerforum-boun...@lists.firesprinkler.org<mailto:sprinklerforum-boun...@lists.firesprinkler.org>>
 On Behalf Of Steve Leyton via Sprinklerforum
Sent: Wednesday, June 24, 2020 4:21 PM
To: 
sprinklerforum@lists.firesprinkler.org<mailto:sprinklerforum@lists.firesprinkler.org>
Cc: Steve Leyton <st...@protectiondesign.com<mailto:st...@protectiondesign.com>>
Subject: Listed sprinkler guard for horizontal or vertical spray sidewalls

Does anyone know if any manufacturers have a listed guard for standard sidewall 
sprinklers?   We specified Viking on a project where the sprinklers are 
installed on the piping, running alongside beams in an open area of a tilt-up 
building that is being repurposed as a charter school, so Light Hazard 
occupancy class.   The client has requested that these particular sprinklers be 
protected from potential damage, but they are already installed so our first 
choice is to find a solution for horizontal sidewalls.   2nd choice is to roll 
the piping and install vertical sidewalls (I think we should have designed it 
that way in the first place in hindsight), so if no guards are available, at 
least the piping will protect the sprinklers.   Any of the manufacturers have a 
listed solution for horizontal or vertical?