You might want to put a handwashing sink in the pump room downstream of the
pump. It seems like adding one toilet to an otherwise stand-alone sprinkler
system, to make it a flow-through system to alleviate the need for a
backflow, at least in Washington, turns it into a plumbing system.



Ron Greenman

rongreen...@gmail.com

253.576.9700

The Universe is monstrously indifferent to the presence of man. -Werner
Herzog, screenwriter, film director, author, actor and opera
director (1942-)


On Wed, Jul 8, 2020 at 11:25 AM Mike B Morey via Sprinklerforum <
sprinklerforum@lists.firesprinkler.org> wrote:

> I would say your own assessment if I understand it, of "it could be a
> private waterworks system if the AHJ approves" is correct.  There is in my
> mind one big caveat beyond approved/not approved by the AHJ and that's the
> reliability of the pump if it is equipped with mechanical seals rather than
> gland packing since it may not being regularly run now that there is no
> domestic usage.  In an ideal world you'd probably put a red pump in, but
> that's obviously not the ideal solution from the owner's perspective.  In
> this situation I'd probably want to sit the owner and AHJ and maybe
> insurance down in a room with yourself.  Arguably whether explicit or
> implicit there's some degree of "it's already there and works" to lend
> credence to it being a "private water supply" but that's above our
> collective pay grade.
>
> ------------------------------
>
> *Mike Morey*
> *CFPS 3229 • NICET S.E.T. 123677*
> *Project Manager* • Fire Protection Group
> * Shambaugh & Son, LP **an EMCOR Company*
> 7614 Opportunity Drive • Fort Wayne, IN • 46825
> *direct *260.487.7824* /  cell *260.417.0625* /  fax *260.487.7991
> * email *mmo...@shambaugh.com
>
>
>
>
>
>
>
> From:        "Reed A. Roisum, SET via Sprinklerforum" <
> sprinklerforum@lists.firesprinkler.org>
> To:        "sprinklerforum@lists.firesprinkler.org" <
> sprinklerforum@lists.firesprinkler.org>
> Cc:        "Reed A. Roisum, SET" <raroi...@kfi-eng.com>
> Date:        07/08/2020 01:01 PM
> Subject:        RE: Pump or Fire Pump
> Sent by:        "Sprinklerforum" <
> sprinklerforum-boun...@lists.firesprinkler.org>
> ------------------------------
>
>
>
> BE ADVISED - This email originated outside EMCOR.
>
>
> There is a couple of small additions to the building and domestic water
> was removed from the system.
>
> That is one question that came up, should the original system have been
> designed with a fire pump as it was for domestic and fire?  The AHJ has not
> approved the system and seems to be questioning whether this should be a
> listed fire pump installed per NFPA 20 or if this is can be looked at as
> though it is like a municipal system until you hit the backflow.
>
>
> Reed A. Roisum, SET *|* *KFI Engineers* *|* Senior Fire Protection
> Designer *|* Fargo, ND *|* *direct:* 701.552.9903* | **mobile:*
> 701.388.1352 *|* *KFIengineers.com*
> <https://urldefense.com/v3/__http://www.kfiengineers.com__;!!FaxH778!NNQ74vO_AftLU_0fnsW8tEIL5qDr5TcoABvnMoFeDuWupg2vjijtkR_YlUOoYgpK$>
> *From:* Sprinklerforum <sprinklerforum-boun...@lists.firesprinkler.org> *On
> Behalf Of *Matt Grise via Sprinklerforum
> * Sent:* Wednesday, July 8, 2020 10:44 AM
> * To:* sprinklerforum@lists.firesprinkler.org
> * Cc:* Matt Grise <m...@afpsprink.com>
> * Subject:* Re: Pump or Fire Pump
>
> what kind of changes are you making to the system? Is this a case where a
> previously approved application is still approved?
>
> Matt
>
> ------------------------------
>
> *From:* Sprinklerforum <*sprinklerforum-boun...@lists.firesprinkler.org*
> <sprinklerforum-boun...@lists.firesprinkler.org>> on behalf of Reed A.
> Roisum, SET via Sprinklerforum <*sprinklerforum@lists.firesprinkler.org*
> <sprinklerforum@lists.firesprinkler.org>>
> * Sent:* Wednesday, July 8, 2020 10:33 AM
> * To:* *sprinklerforum@lists.firesprinkler.org*
> <sprinklerforum@lists.firesprinkler.org> <
> *sprinklerforum@lists.firesprinkler.org*
> <sprinklerforum@lists.firesprinkler.org>>
> * Cc:* Reed A. Roisum, SET <*raroi...@kfi-eng.com* <raroi...@kfi-eng.com>>
> * Subject:* Pump or Fire Pump
>
> I have a project where there is an existing domestic pump and water
> storage tanks.  They used to serve both domestic and fire protection in a
> group of buildings but are no longer being used for domestic but fire
> protection only.  The pump is not a fire pump.  Does it need to be?
>
> There is a building 1,000 feet from the protected buildings that houses
> the pump and tanks.  The pump charges a 3” underground that supplies
> multiple buildings that each have their own backflow assembly and riser.
> In my mind, it is basically the same set up as a municipal system, but
> instead of doing a flow test at the hydrant outside of the building to find
> my water supply, I look at the pump curve and design back to the pump.  The
> other thought I had, was that this system is now to supply water only for
> the fire protection system so now I need to demo that perfectly adequate
> pump and replace it with a red one to meet the codes/standards.
>
> Looking at NFPA 13, 2016 edition, Chapter 24 Water Supplies, they list
> acceptable water supplies for sprinkler systems…
> One acceptable arrangement is “A connection to an *approved *public or*
> private waterworks system* in accordance with 24.2.2”.
> 24.2.2 seems to just require that you are connected to a “reliable
> waterworks system”.
>
> Just wondering if my existing tank and pump arrangement could be
> considered a reliable private waterworks system?  I guess that is up to the
> discretion of the AHJ?
>
> *NFPA 13, 2016 edition*
> *Chapter 24 Water Supplies*
> *24.1 General.*
> *24.2 Types.*
> *24.2.1*** Water supplies for sprinkler systems shall be one of the
> following or any combination:*
> *(1) A connection to an approved **public or private waterworks system**
> in accordance with 24.2.2*
> *(2) A connection including a fire pump in accordance with 24.2.3*
> *(3) A connection to a water storage tank at grade or below grade
> installed in accordance with NFPA 22 and filled from an approved source*
> *(4) A connection to a pressure tank in accordance with 24.2.4 and filled
> from an approved source*
> *(5) A connection to a gravity tank in accordance with 24.2.5 and filled
> from an approved source*
> *(6) A penstock, flume, river, lake, pond, or reservoir in accordance with
> 24.2.6*
> *(7)*A source of recycled or reclaimed water where the building owner (or
> their agent) has analyzed the source of the water and the treatment process
> (if any) that the water undergoes before being made available to the
> sprinkler system and determined that any materials, chemicals, or
> contaminants in the water will not be detrimental to the components of the
> sprinkler system it comes in contact with*
> *24.2.2* Connections to Waterworks Systems.*
> *24.2.2.1*
> <https://urldefense.com/v3/__http://24.2.2.1__;!!FaxH778!NNQ74vO_AftLU_0fnsW8tEIL5qDr5TcoABvnMoFeDuWupg2vjijtkR_YlY6ryKrT$>*
> A connection to a reliable waterworks system shall be an acceptable water
> supply source.*
> *24.2.2.2*** The volume and pressure of a public water supply shall be
> determined from waterflow test data or other approved method.*
> *24.2.3* Pumps**. A single automatically controlled fire pump installed
> in accordance with NFPA 20 shall be an acceptable water supply source*
>
> I couldn’t find a definition of ‘waterworks’ in NFPA or IBC.
> BTW, 2018 IBC is applicable.
>
> Any help or code/standard references are appreciated.
>
> Thank you.
> Reed Roisum
>
>
> Reed A. Roisum, SET *|* *KFI Engineers* *|* Senior Fire Protection
> Designer *|* Fargo, ND *|* *direct:* 701.552.9903* | **mobile:*
> 701.388.1352 *|* *KFIengineers.com*
> <https://urldefense.com/v3/__https://linkprotect.cudasvc.com/url?a=http*3a*2f*2fwww.kfiengineers.com&c=E,1,mxirS9-jVuw4dWsfp1GyRgcLdwU7Ve5QIKz9dp5KG0h8DmyYvblK1s3eodTtkMNwVwuAzEu9yssg_Koy0TIZGuwlypQFDIiAkoxHKlVtWzOk9KU,&typo=1__;JSUl!!FaxH778!NNQ74vO_AftLU_0fnsW8tEIL5qDr5TcoABvnMoFeDuWupg2vjijtkR_YlS_r2hwS$>
> _______________________________________________
> Sprinklerforum mailing list
> Sprinklerforum@lists.firesprinkler.org
>
> https://urldefense.com/v3/__http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org__;!!FaxH778!NNQ74vO_AftLU_0fnsW8tEIL5qDr5TcoABvnMoFeDuWupg2vjijtkR_Yldab_XIj$
>
> This message is for the named person's use only. It may contain
> confidential, proprietary or legally privileged information. No
> confidentiality or privilege is waived or lost by any mistransmission. If
> you receive this message in error, please immediately delete it and all
> copies of it from your system, destroy any hard copies of it and notify the
> sender. You must not, directly or indirectly, use, disclose, distribute,
> print, or copy any part of this message if you are not the intended
> recipient.
> _______________________________________________
> Sprinklerforum mailing list
> Sprinklerforum@lists.firesprinkler.org
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>
>
_______________________________________________
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to