Section 9.3.2 was added in the 2019 edition of NFPA 13R and could apply to
the demand in addition to the design sprinklers:


*9.3.1 For systems with common domestic/fire mains serving more than one
dwelling unit, domestic demand for the building being calculated shall be
included as part of the overall system demand unless provisions are made to
prevent the domestic waterflow on sprinkler system activation.*


The 2019 edition of NFPA 13 has language that may also be applicable:


*5.1.3.3 Where a single main less than 4 in. (100 mm) in diameter serves
both fire systems and other uses, the non-fire demand shall be added to the
hydraulic calculations for the fire system at the point of connection
unless provisions have been made to automatically isolate the non-fire
demand during a fire event.*


It would be the owner's or owner's agent's (engineer of record)
responsibility to make any applicable water supply adjustments per Section
4.2.


Kevin Hall, P.E., MSFPE
*Coordinator, Engineering and Technical Services*

*American Fire Sprinkler Association*
p: 214-349-5971
w: firesprinkler.org
<https://www.facebook.com/firesprinkler.org/>
<https://twitter.com/afsa/status/1039528345367732224>
<https://www.linkedin.com/company/american-fire-sprinkler-association-afsa-/>
   <https://www.instagram.com/firesprinklerorg/>


*AFSA Summer Sale!*

For a limited time only, AFSA is offering members up to 50% off its
on-demand recorded webinars! Featuring the most sought-after thought
leaders, AFSA On-Demand offers a superior learning experience with ability
to earn CEU and CPD credits anytime, anywhere. Visit
http://www.firesprinkler.org/ondemand to learn more.



On Thu, Sep 10, 2020 at 12:28 PM Hinson, Ryan via Sprinklerforum <
[email protected]> wrote:

> We have run into a dock FW system design where multiple automatic flushing
> valves are being provided on the system to prevent freezing by
> automatically flowing water at temps below 40°F to the order of 300 gpm.
> Though this flow should absolutely be included in the system demand flow, I
> am having difficulty finding code direction requiring its inclusion in
> hydraulic demands other than where NFPA 13R systems may have to account for
> concurrent domestic flows.
>
> Any code sections come to mind?
>
> Ryan L. Hinson, PE*, SET**  \  Burns & McDonnell
> Senior Fire Protection Engineer, Fire Protection Engineering Group
> O 952-656-3662 \  M 763-688-4045 \  F 952-229-2923
> [email protected]<mailto:[email protected]>  \  burnsmcd.com<
> http://www.burnsmcd.com/>
> 8201 Norman Center Drive, Suite 500  \  Minneapolis-St. Paul, MN 55437
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to