This may or may not be helpful:

IBC 2018 (see exceptions below)


*507.4 Sprinklered, One-Story Buildings*

The area of a Group A-4
<https://up.codes/viewer/wyoming/ibc-2018/chapter/3/occupancy-classification-and-use#303.5>
building
not more than one story above grade plane
<https://up.codes/viewer/wyoming/ibc-2018/chapter/2/definitions#story_above_grade_plane>
of
other than Type V construction, or the area of a Group B
<https://up.codes/viewer/wyoming/ibc-2018/chapter/3/occupancy-classification-and-use#304>,
F, M or S building no more than one story above grade plane
<https://up.codes/viewer/wyoming/ibc-2018/chapter/2/definitions#story_above_grade_plane>
of
any construction type, shall not be limited where the building is provided
with an automatic sprinkler system
<https://up.codes/viewer/wyoming/ibc-2018/chapter/2/definitions#automatic_sprinkler_system>
throughout
in accordance with Section 903.3.1.1
<https://up.codes/viewer/wyoming/ibc-2018/chapter/9/fire-protection-and-life-safety-systems#903.3.1.1>
and
is surrounded and adjoined by public ways
<https://up.codes/viewer/wyoming/ibc-2018/chapter/2/definitions#public_way>
 or yards
<https://up.codes/viewer/wyoming/ibc-2018/chapter/2/definitions#yard> not
less than 60 feet (18 288 mm) in width.


*Exceptions:*

   1. Buildings and structures of Type I or II construction for rack
   storage facilities
   <https://up.codes/viewer/wyoming/ibc-2018/chapter/2/definitions#facility>
that
   do not have access by the public shall not be limited in height, provided
   that such buildings conform to the requirements of Sections 507.4 and
   903.3.1.1
   
<https://up.codes/viewer/wyoming/ifc-2018/chapter/9/fire-protection-and-life-safety-systems#903.3.1.1>
    and Chapter 32
   
<https://up.codes/viewer/wyoming/ifc-2018/chapter/32/high-piled-combustible-storage#32>
of
   the *International Fire Code <https://up.codes/viewer/wyoming/ifc-2018>*.
   2.
   The automatic sprinkler system
   
<https://up.codes/viewer/wyoming/ibc-2018/chapter/2/definitions#automatic_sprinkler_system>
shall
   not be required in areas occupied for indoor participant sports, such as
   tennis, skating, swimming and equestrian activities in occupancies in Group
   A-4
   
<https://up.codes/viewer/wyoming/ibc-2018/chapter/3/occupancy-classification-and-use#303.5>,
   provided that all of the following criteria are met:
   1. 2.1. Exit
      <https://up.codes/viewer/wyoming/ibc-2018/chapter/2/definitions#exit>
doors
      directly to the outside are provided for occupants of the participant
      sports areas.
      2. 2.2. The building is equipped with a fire alarm system
      
<https://up.codes/viewer/wyoming/ibc-2018/chapter/2/definitions#fire_alarm_system>
       with manual fire alarm boxes
      
<https://up.codes/viewer/wyoming/ibc-2018/chapter/2/definitions#manual_fire_alarm_box>
installed
      in accordance with Section 907
      
<https://up.codes/viewer/wyoming/ibc-2018/chapter/9/fire-protection-and-life-safety-systems#907>
      .
      3. 2.3. An automatic sprinkler system
      
<https://up.codes/viewer/wyoming/ibc-2018/chapter/2/definitions#automatic_sprinkler_system>
is
      provided in storage rooms, press boxes, concession booths or other spaces
      ancillary to the sport activity space.



Ron Greenman

rongreen...@gmail.com

253.576.9700

The Universe is monstrously indifferent to the presence of man. -Werner
Herzog, screenwriter, film director, author, actor and opera
director (1942-)


On Tue, Dec 1, 2020 at 10:11 AM Travis Mack via Sprinklerforum <
sprinklerforum@lists.firesprinkler.org> wrote:

> I seem to recall something in the I-codes that states you are not required
> to protect over an event center floor if the ceiling/roof is "x feet" above
> the floor level.  However, of course, I can't locate the reference section
> today.  Does anyone happen to know where that reference may be at in the
> I-codes?
>
>
> Travis Mack, CFPS, CWBSP, RME-G, SET
> Engineering Manager
> MFP Design
> 3356 E Vallejo Ct
> Gilbert, AZ 85298
> NEW EXTENSION: 480-505-9271 ext. 700
> NEW MOBILE: 480-272-2471
> travis.m...@mfpdesign.com
> www.mfpdesign.com
>
> Send large files to us via: https://www.hightail.com/u/MFPDesign
> LinkedIn: https://www.linkedin.com/in/travismack
>
>
> _______________________________________________
> Sprinklerforum mailing list
> Sprinklerforum@lists.firesprinkler.org
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>
_______________________________________________
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org