Depending on your elevation above MSL, you should be fine based on the 
atmospheric pressure.
  

  
  
  

  
  
>   
> On Dec 4, 2020 at 4:57 PM,  <Steven Jenkins via Sprinklerforum 
> (mailto:[email protected])>  wrote:
>   
>   
>   
>  We have an existing horizontal split case fire pump and ground level water 
> storage tank. The storage in the protected building is changing, and the 
> amount of water needed for fire protection is going up. We are changing the 
> tank to a “break tank”, but even then there is not much water left in the 
> tank after the required supply duration, only a few feet left in the bottom 
> of the tank. The pump is right next to the tank, so not much loss due to 
> friction in the connecting pipe. With the tank full, before the pump is 
> turned on, the gauge on the suction side reads about 15 psi, due to the 
> height of water in the tank. When the pump is running at 150%, this drops to 
> about 7.5 psi. At the end of the required duration I will only have about 1.5 
> psi of head from the height of water in the tank. So if I lose another 7.5 
> with the pump on, the gauge would read -6 psi. Is this a problem for 
> compliance with 2019 NFPA 20, or since the pump is already running does this 
> make the negative 6 psi gauge reading OK? 2019 NFPA 20 4.16.3.2 Thanks, J 
> _______________________________________________ Sprinklerforum mailing list  
> [email protected] 
> (mailto:[email protected])   
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org  
>  
>
>   
  
  
     