Very good question.  I've read discussions on this issue recently as well and 
really wonder what was the thought process behind including a non-existent flow 
value in the system design and calculations.

I would love to hear the rationale for this section.


Craig Prahl | Jacobs | Group Lead/SME - Fire Protection | 864.676.5252 | 
[email protected] | www.jacobs.com
1041 East Butler Road   Greenville, South Carolina  29606

-----Original Message-----
From: Sprinklerforum <[email protected]> On Behalf 
Of James Litvak via Sprinklerforum
Sent: Thursday, December 10, 2020 10:45 AM
To: [email protected]
Cc: James Litvak <[email protected]>
Subject: [EXTERNAL] 23.4.4.2.5: What is the purpose and how does it apply?

I've just been introduced to section 23.4.4.2.5 (2016). In my particular 
situation, I have an EH2 refueling building (0.4 / 2,500) that is 2,268 sq.ft. 
in its entirety. The flow from my calc came out to 998 gpm, so I was told by my 
coworker who reviewed my plans not to worry about the extra 2 gpm that would 
need to be added to meet the 0.4 * 2,500 = 1,000 gpm minimum requirement. 
However, this is a dry system. So I asked my coworker if
23.4.4.2.5 applies to the 2,500 sq.ft. minimum per Figure 11.2.3.1.1, or if it 
applies to 3,250 sq.ft. after I increase 30%, which would require a minimum of 
1,300 gpm. Not only are we unsure of that, but that got us wondering what the 
exact purpose of this section is, and how it would apply to other situations. 
If I have an EH2 building that is 300 sq.ft. and protected with 3 sprinklers on 
a dry system, do I need to design the riser and cross main to handle 1,000 
(maybe 1,300) gpm? That seems insane.

I've read through some threads on this forum, and also some websites, and the 
example often given is that of a paint booth. One example considers a paint 
booth protected by 6 high temp. sprinklers with a demand of 250 gpm.
It says that 550 gpm would need to be added to the cross main to make up the 
rest of the required 0.4 * 2,000 = 800 gpm minimum demand. But why? If a 
sprinkler in an EH2 area is required to provide at least 0.4 gpm/sq.ft., and 
they are doing that, what is the purpose of providing more flow? The hazard 
remains the exact same, so why are we required to overdischarge, when the 
actual potential risk is lower than a larger area? Theoretically, my 2,268 EH2 
building is a lower risk than a 4,000 EH2 building that is otherwise exactly 
the same. Yet if I go by 1,300 gpm as my minimum required demand, I will be 
providing way more water per sq.ft. in the smaller building than in the larger 
building.

So unless I am completely missing something here - or a few things - I am 
totally baffled. I'm hoping someone can help me understand all this.
Thanks.


James Litvak
_______________________________________________
Sprinklerforum mailing list
[email protected]
https://urldefense.com/v3/__http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org__;!!B5cixuoO7ltTeg!VO4VMIa80RQe-j4UNMGpQfWegM4j7sqJxkum95ViMHfpMByNGKHBmRo-w194r6keuQ$

________________________________

NOTICE - This communication may contain confidential and privileged information 
that is for the sole use of the intended recipient. Any viewing, copying or 
distribution of, or reliance on this message by unintended recipients is 
strictly prohibited. If you have received this message in error, please notify 
us immediately by replying to the message and deleting it from your computer.
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to