It is and has been surprising to me when fire protection contractors ask the 
pipe freezing question or when they ask piping support questions in context 
with approval by local AHJ of any kind. The reason for the surprise is because 
contractors have ready access to materials, labor and space to conduct their 
own very convincing freeze tests or load tests.
The pipe freezing question is often asked. The mechanics of why piping systems 
fail due to freezing is documented to be the result of excessive water pressure 
in the unfrozen part of a water piping system. Pipe failure is not due to the 
conventional wisdom idea that ice expands against the piping. The frozen part 
is a solid ice plug that occupies more volume than the original liquid water 
volume that has frozen. Since the unfrozen water is not compressible that 
increase volume change of the now frozen water results in excessive pressure in 
the remaining piping.
Notice where an antifreeze hose cock fails that has frozen because the outside 
hose was never removed for the winter trapping water within the assembly. It 
fails at the assembly part farthest into the building where the assembly was 
the warmest, not at the colder section closer to the building exterior. 
Ask some of your plumber friends, perhaps the older ones, if they have ever 
seen dry ice packed around a water service line as a way to shutoff the water 
when the service tap valve cannot be found or is not functioning. This method 
works well as long as the excess down stream pressure is monitored and is 
periodically removed by cracking a valve open.
A simple experiment demonstrates the freezing mechanics. Here is a link to one 
performed at a university in Wisconsin.
https://www.madisongroup.com/publications/StudyofFreezing.pdf 
<https://www.madisongroup.com/publications/StudyofFreezing.pdf>
Another information source is here from Illinois: 
https://www.ideals.illinois.edu/handle/2142/54757 
<https://www.ideals.illinois.edu/handle/2142/54757>
A fire protection contractor with any doubts (I would have doubts and I would 
want to see it myself.) could easily fabricate a small jungle gym of scrap 
piping, fittings and used sprinklers to setup outside the shop for testing the 
condition of residual water freezing in sprinkler drops.
Regarding load testing, it was common practice many years ago to build a small 
structural part of a building and then load it up with tons of whatever 
material was on hand to prove strength beyond that required for the structure. 
There is not much tech required to tally up the weights applied. Load tests for 
fire protection components would be much less elaborate. For a very simple 
example, if an AHJ questions how strong some twisted wire bracing is, then mock 
up a simple seat suspended by the practice for the AHJ to sit on. Contractors 
also have the means they did not have tears ago to use smart phones to record 
their testing methods.

Allan Seidel
St. Louis, MO