To my knowledge, the 2 hole strap is listed as a hanger only. Not for seismic.

The second question is a good one.
I love Chapter 3, especially for seismic.

Check 3.5.11 in the 2016 for a "Sprig".

The standard mandates riser for 4 way if they exceed 3'-0".

Riser Nipples, the piece between a Cross Main and Branchline, 3.5.9, are 
excluded.

3.5.10 is for "Risers".

Given that the definition of a sprig, seems different than Riser, you may have 
a point.

But Riser is pretty broad.

R/
Matt





-----Original Message-----
From: Sprinklerforum <[email protected]> On Behalf 
Of J H via Sprinklerforum
Sent: Wednesday, December 30, 2020 12:13 PM
To: [email protected]
Cc: J H <[email protected]>
Subject: CPVC EQ Bracing - 2 hole straps and another question

Hello,
I thought that two hole straps used to secure CPVC acted as seismic bracing? I 
don't know where I've heard that and couldn't find anything in the standard. Is 
this correct?

Also, if you have a 1"x8'-6" riser to a single horizontal sidewall sprinkler 
would that technically be an 'armover' and not require seismic or would that 
fall under being a riser requiring seismic bracing?

Thanks,
JH

<https://www.avast.com/sig-email?utm_medium=email&utm_source=link&utm_campaign=sig-email&utm_content=webmail&utm_term=icon>
Virus-free.
www.avast.com
<https://www.avast.com/sig-email?utm_medium=email&utm_source=link&utm_campaign=sig-email&utm_content=webmail&utm_term=link>
<#DAB4FAD8-2DD7-40BB-A1B8-4E2AA1F9FDF2>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to