I think I'd try to get the building designer to put the UPS into a
dedicated enclosure and use an inerting system.

On Thu, Jan 14, 2021 at 10:48 AM Prahl, Craig/GVL via Sprinklerforum <
sprinklerforum@lists.firesprinkler.org> wrote:

> So, I'll assume this battery assembly will be in some type of occupiable
> enclosure which will have environmental control.
>
> I would definitely not extend or try to tie it into any existing PreAction
> system.
>
> I would be looking at a stand alone suppression system, either clean agent
> or aerosol depending on the battery chemistry.
>
> I'd also be sure to run my idea past the local fire code official.
>
> Depending on the unknowns, there may be Code requirements for separation
> to adjacent occupied buildings.
>
> Craig Prahl | Jacobs | Group Lead/SME - Fire Protection |
> craig.pr...@jacobs.com | www.jacobs.com
> 1041 East Butler Road   Greenville, South Carolina  29606
> CONTACT BY: email or MS TEAMS
>
> -----Original Message-----
> From: Sprinklerforum <sprinklerforum-boun...@lists.firesprinkler.org> On
> Behalf Of Steve Leyton via Sprinklerforum
> Sent: Thursday, January 14, 2021 1:18 PM
> To: sprinklerforum@lists.firesprinkler.org
> Cc: Steve Leyton <st...@protectiondesign.com>; Matt Grise <
> m...@afpsprink.com>
> Subject: [EXTERNAL] RE: Stand-Alone UPS protection design
>
> No idea, but I'll ask.   Looking for wide-tooth comb here.   Are wet-chem
> systems the "usual" go-to or is it more nuanced than that?
>
> SL
>
> -----Original Message-----
> From: Sprinklerforum [mailto:
> sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of Matt Grise
> via Sprinklerforum
> Sent: Thursday, January 14, 2021 10:17 AM
> To: sprinklerforum@lists.firesprinkler.org
> Cc: Matt Grise <m...@afpsprink.com>
> Subject: Re: Stand-Alone UPS protection design
>
> What is the battery chemistry?
>
>
>
> Matt Grise
> Alliance Fire Protection
> m 913 526 7443
> o 913 888 0647
> f 913 888 0618
>
> Sent from mobile device
>
>
> -------- Original message --------
> From: Steve Leyton via Sprinklerforum <
> sprinklerforum@lists.firesprinkler.org>
> Date: 1/14/21 12:15 PM (GMT-06:00)
> To: "Prahl, Craig/GVL" <craig.pr...@jacobs.com>,
> sprinklerforum@lists.firesprinkler.org
> Cc: Steve Leyton <st...@protectiondesign.com>
> Subject: RE: Stand-Alone UPS protection design
>
> I can't tell you the exact dimensions for specifications because it's in
> pre-design.   It's right next to the building, but several hundred feet
> from the existing preaction areas and riser.
>
> -----Original Message-----
> From: Prahl, Craig/GVL [mailto:craig.pr...@jacobs.com]
> Sent: Thursday, January 14, 2021 10:02 AM
> To: sprinklerforum@lists.firesprinkler.org
> Cc: Steve Leyton <st...@protectiondesign.com>
> Subject: RE: Stand-Alone UPS protection design
>
> Steve,
>
> Can you provide a better description of this unit?  How far from the
> building will it be located?
>
> Craig Prahl | Jacobs | Group Lead/SME - Fire Protection |
> craig.pr...@jacobs.com | http://www.jacobs.com<http://www.jacobs.com>
> 1041 East Butler Road   Greenville, South Carolina  29606
> CONTACT BY: email or MS TEAMS
>
> -----Original Message-----
> From: Sprinklerforum <sprinklerforum-boun...@lists.firesprinkler.org> On
> Behalf Of Steve Leyton via Sprinklerforum
> Sent: Thursday, January 14, 2021 12:58 PM
> To: sprinklerforum@lists.firesprinkler.org
> Cc: Steve Leyton <st...@protectiondesign.com>
> Subject: [EXTERNAL] Stand-Alone UPS protection design
>
> I'm engaged in a conversation with a project team where an Uninterrupted
> Power Supply is being added to a local small-scale broadcast facility (NPR
> affiliate).   The control rooms and studios are already protected by
> preaction and this battery stack is being added outside the building and a
> ways away from the existing preaction areas.   The two candidate designs
> are to extend the preaction or use a pre-engineered wet-chem system and I'd
> love for any and everyone who has experience with this type of hazard to
> chime in on whether there is a preferred or "best" practice.   My feeling
> is that a wet-chem system is the way to go and the most common practice -
> can anyone verify or do I have that wrong.
>
> Fire away please...
>
> Steve L.
>
>
> _______________________________________________
> Sprinklerforum mailing list
> Sprinklerforum@lists.firesprinkler.org
>
> https://urldefense.com/v3/__https://linkprotect.cudasvc.com/url?a=https*3a*2f*2furldefense.com*2fv3*2f__http*3a*2f*2flists.firesprinkler.org*2flistinfo.cgi*2fsprinklerforum-firesprinkler.org__*3b*21*21B5cixuoO7ltTeg*21RBqeKKjG60wNEVmjtlo8VtJ_60JAV9CUPjj0pGiQ2Zgf2T3xTnT90OKuOqUcJqL9Og*24&c=E,1,BShkYLUD1RLgiLgDZGfVDk05i6BwISef9l7ExjaBxbFy7ewEqpj8ib6K71px8n-sK6S7gUdeT6GDk8c14yvp5IoHcjSWkVv9opvRudfz_gA,&typo=1__;JSUlJSUlJSUlJSUlJSUl!!B5cixuoO7ltTeg!WnEdr_kQ8BS7DlJAQTQDpT_Nk7E_rYIwlR9sVT1JgeBai3CzHDiG10rasN00-3g2aA$
>
> ________________________________
>
> NOTICE - This communication may contain confidential and privileged
> information that is for the sole use of the intended recipient. Any
> viewing, copying or distribution of, or reliance on this message by
> unintended recipients is strictly prohibited. If you have received this
> message in error, please notify us immediately by replying to the message
> and deleting it from your computer.
> _______________________________________________
> Sprinklerforum mailing list
> Sprinklerforum@lists.firesprinkler.org
>
> https://urldefense.com/v3/__https://linkprotect.cudasvc.com/url?a=http*3a*2f*2flists.firesprinkler.org*2flistinfo.cgi*2fsprinklerforum-firesprinkler.org&c=E,1,1rqBO1RPcsDBQA_1RsOtIDA7HU6n8bYXLlak9kAhj6-rYZ6SR1DJhaMaJIcjiMN_90Zer0oMKr5S7rwTWXfdqEEzeg7GgEUMA-uY0WvKVUPOs8w8&typo=1__;JSUlJSU!!B5cixuoO7ltTeg!WnEdr_kQ8BS7DlJAQTQDpT_Nk7E_rYIwlR9sVT1JgeBai3CzHDiG10rasN34w3auUA$
> _______________________________________________
> Sprinklerforum mailing list
> Sprinklerforum@lists.firesprinkler.org
>
> https://urldefense.com/v3/__http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org__;!!B5cixuoO7ltTeg!WnEdr_kQ8BS7DlJAQTQDpT_Nk7E_rYIwlR9sVT1JgeBai3CzHDiG10rasN3MNNN8gQ$
> _______________________________________________
> Sprinklerforum mailing list
> Sprinklerforum@lists.firesprinkler.org
>
> https://urldefense.com/v3/__http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org__;!!B5cixuoO7ltTeg!WnEdr_kQ8BS7DlJAQTQDpT_Nk7E_rYIwlR9sVT1JgeBai3CzHDiG10rasN3MNNN8gQ$
>
> ________________________________
>
> NOTICE - This communication may contain confidential and privileged
> information that is for the sole use of the intended recipient. Any
> viewing, copying or distribution of, or reliance on this message by
> unintended recipients is strictly prohibited. If you have received this
> message in error, please notify us immediately by replying to the message
> and deleting it from your computer.
> _______________________________________________
> Sprinklerforum mailing list