You might want to look at the ROC for 2013, "non-combustible and limited 
combustible" was specifically removed during the revision process.  Excerpt 
from the substantiation: 

"The requirement for non-combustible or limited combustible materials is not 
important. Baffles can be made of wood or even plastic as long as they stay in 
place long enough for the sprinkler to open. The issue is that they be solid 
(with no holes that would let the water through) and rigid (so that they do not 
blow over due to the force of the hot gasses from the fire or the force of the 
water spray hitting them). If the water spray is impacting the combustible 
baffle, it will keep it from burning. If the water spray is not impacting the 
baffle, it will not matter if the baffle goes away because it was not stopping 
the spray of water anyway."

Mike Morey
CFPS 3229 . NICET S.E.T. 123677
Project Manager . Fire Protection Group
Shambaugh & Son, LP an EMCOR Company
7614 Opportunity Drive . Fort Wayne, IN . 46825 direct 260.487.7824 /  cell 
260.417.0625 /  fax 260.487.7991 email [email protected]



-----Original Message-----
From: Sprinklerforum <[email protected]> On Behalf 
Of Matthew J Willis via Sprinklerforum
Sent: Tuesday, March 9, 2021 12:43 PM
To: [email protected]
Cc: Matthew J Willis <[email protected]>
Subject: I'm Baffled

 
BE ADVISED - This email originated outside EMCOR. 
 

2019

10.2.5.4.2 (Concerning baffles for cold solder)

It screams metal at me.
However, would you think that plywood meets this?

R/
Matt



Matthew J. Willis, CWBSP
Design Manager / 3-D Specialist
1530 Samco Road, Rapid City, SD 57702
Office-605.348.2342 /Direct-605.593.5063/Cell-605.391.2733  






_______________________________________________
Sprinklerforum mailing list
[email protected]
https://urldefense.com/v3/__http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org__;!!FaxH778!NeboJArRDRbMFxHTOQ-3TTNh71fLoCUEtHC0HvdxcA2PNo52m2YdGY-6YyVvx3ud$
 

This message is for the named person's use only.  It may contain confidential, 
proprietary or legally privileged information. No confidentiality or privilege 
is waived or lost by any mistransmission.  If you receive this message in 
error, please  immediately delete it and all copies of it from your system, 
destroy any hard copies of it and notify the sender.  You must not, directly or 
indirectly, use, disclose, distribute, print, or copy any part of this message 
if you are not the intended recipient.
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to