We've typically installed a ball drip in gravel similar to a french drain
at the low point.

On Wed, Mar 10, 2021 at 11:17 AM Dewayne Martinez via Sprinklerforum <
[email protected]> wrote:

> I see a trend starting in our area where the architect is specifying a
> remote free standing FDC without a valve pit when the check valve can be
> placed inside the building. Upon talking to my field superintendent he was
> concerned that some check valves let multiple gallons of water through
> whenever a system is drained and refilled and that the remote pipe may
> eventually fill up and freeze.  We were toying with the idea of installing
> a return bend in the FDC pipe downstream of the check before it leaves the
> building to help prevent this.  A  ball valve would be installed between
> the return bend and check to drain out the pipe.  Anyone else have insight
> on this?
>