That wording has been updated on Potters flow switch I believe it's only the 
drain valve needs to be 24" away.
When I spoke to a  tech rep about that they said because it’s a UL list 
assembly it was acceptable.

Jerry Van Kolken
Millennium Fire Protection Corp.
2950 San Luis Rey Rd.
Oceanside, CA 92058
(760) 722-2722 FX 722-2730

-----Original Message-----
From: Sprinklerforum <[email protected]> On Behalf 
Of Matthew J Willis via Sprinklerforum
Sent: Monday, March 15, 2021 3:45 PM
To: [email protected]
Cc: Matthew J Willis <[email protected]>
Subject: RE: Check Valve After Flow switch?

I would as well.

What happened to the "not within 24" of a drain or valve?"

A check valve is a valve.. Right?

R/
Matt

-----Original Message-----
From: Sprinklerforum <[email protected]> On Behalf 
Of John Denhardt via Sprinklerforum
Sent: Monday, March 15, 2021 3:36 PM
To: [email protected]
Cc: John Denhardt <[email protected]>
Subject: Re: Check Valve After Flow switch?

I would like to know why this is the "best way" for the installation.  I am not 
stating it is not, just not sure why one way is better especially since we have 
done it a certain way for years.

Thanks,
John

John August Denhardt, PE
*Vice President, Engineering and Technical Services*

*American Fire Sprinkler Association*
m: p: 301-343-1457
214-349-5965 ext 121
w: firesprinkler.org
<https://www.facebook.com/firesprinkler.org/>
<https://twitter.com/afsa/status/1039528345367732224>
<https://www.linkedin.com/company/american-fire-sprinkler-association-afsa-/>
   <https://www.instagram.com/firesprinklerorg/>

*Our members are at the heart of everything we do*


*Expand your business with ITM*
Professionalize the role of your inspection team with AFSA’s ITM Inspector 
Development Program. This comprehensive 20-month program provides a blended 
learning environment teamed with robust curriculum created by top industry 
leaders. Plus, the first six-months of instruction is online. Now enrolling for 
Spring 2021 <https://www.firesprinkler.org/itm>.




On Mon, Mar 15, 2021 at 5:05 PM Henry Fontana via Sprinklerforum < 
[email protected]> wrote:

> Hello all.
>
> This is not a code change. Both manufacturers (one of them I work for)
> state that this is the best way for installation and will not cause a
> nuisance alarm. Ever since Globe came out with theirs I have
> questioned why it’s designed this way.
>
> Henry Fontana
> Operations Manager (NYC)
> Johnson Controls Fire Protection
> 100 Lighting Way| St#402|Secaucus|NJ
> 07094<x-apple-data-detectors://2/0>
> Cell: 201-210-9873<tel:201-210-9873>
> [email protected]<mailto:[email protected]>
>
>
> On Mar 15, 2021, at 5:01 PM, Jerry Van Kolken via Sprinklerforum <
> [email protected]> wrote:
>
> I've just received a second product sheet from a different suppliers
> for a pre-built riser where the check valve is located above/after the
> flow switch. Is this arrangement a new change coming is the code?
>
> Jerry Van Kolken
> Millennium Fire Protection Corp.
> 2950 San Luis Rey Rd.
> Oceanside, CA 92058
> (760) 722-2722 FX 722-2730
>
> CONFIDENTIALITY NOTICE This e-mail and any attachments are for the
> sole use of the intended recipients and contain information that may
> be confidential or legally privileged. If you have received this
> e-mail in error, please notify the sender by reply e-mail and delete
> the message. Any disclosure, copying, distribution, or use of this
> communication by someone other than the intended recipient is prohibited.
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
> https://nam02.safelinks.protection.outlook.com/?url=http%3A%2F%2Flists
> .firesprinkler.org%2Flistinfo.cgi%2Fsprinklerforum-firesprinkler.org&a
> mp;data=04%7C01%7CHenry.Fontana%40jci.com%7C26515cca58bc49e3d54708d8e7
> f57436%7Ca1f1e2147ded45b681a19e8ae3459641%7C0%7C1%7C637514388691689096
> %7CUnknown%7CTWFpbGZsb3d8eyJWIjoiMC4wLjAwMDAiLCJQIjoiV2luMzIiLCJBTiI6I
> k1haWwiLCJXVCI6Mn0%3D%7C1000&amp;sdata=YJtrVeB3%2B0j7oRNOyglmknAuIy16Q
> %2FWqp4aW3J8goyQ%3D&amp;reserved=0
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
> er.org
>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
CONFIDENTIALITY NOTICE This e-mail and any attachments are for the sole use of 
the intended recipients and contain information that may be confidential or 
legally privileged. If you have received this e-mail in error, please notify 
the sender by reply e-mail and delete the message. Any disclosure, copying, 
distribution, or use of this communication by someone other than the intended 
recipient is prohibited.
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to