Hello Matt I was working in a data center where the customer was very hydrophobic so we decided to use the "dry" flex pendants. They worked very well and in case of an accidental dump of the system their would be no trapped water.
Henry Fontana Operations Manager (NYC) Johnson Controls Fire Protection 100 Lighting Way Secaucus, NJ 07094 Cell: 201-210-9873 [email protected] -----Original Message----- From: Sprinklerforum <[email protected]> On Behalf Of Matt Grise via Sprinklerforum Sent: Wednesday, March 24, 2021 12:43 PM To: [email protected] Cc: Matt Grise <[email protected]> Subject: flex drops on return bend I am looking at a library that is protected by a pre-action system with pendants on return bends. I was thinking about using flex drops in the drop portion of the return bend for ease of testing and center of tile. The flex drops are listed for use in dry systems - so I can't think of any code reason not to do it. Has anyone used flex drops in pre-action or dry systems before? Any issues? Matt _______________________________________________ Sprinklerforum mailing list [email protected] https://nam02.safelinks.protection.outlook.com/?url=http%3A%2F%2Flists.firesprinkler.org%2Flistinfo.cgi%2Fsprinklerforum-firesprinkler.org&data=04%7C01%7CHenry.Fontana%40jci.com%7C3a2306ea775945d6cf6308d8eee3de8e%7Ca1f1e2147ded45b681a19e8ae3459641%7C0%7C1%7C637522009742840055%7CUnknown%7CTWFpbGZsb3d8eyJWIjoiMC4wLjAwMDAiLCJQIjoiV2luMzIiLCJBTiI6Ik1haWwiLCJXVCI6Mn0%3D%7C3000&sdata=eBCyi1qcau5Lm4fQWmqs5DI8u4nvSY7bvEUW4eMa0qk%3D&reserved=0 _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org