NFPA 25 2014 Edition, section 13.6.2.1

I have a 6” Ames 2000 SS that I need to forward flow test. Down stream of the 
#2 OS&Y control valve I have a 6” elbow, a 12” section of 6” pipe on the 
vertical, Then a 6x6x4 tee (4” to the FDC), then on top if the Tee a 6 “ dry 
valve.  13.6.2.1 says we shall exercise annually at minimum flow rate of the 
system demand.  But guess what. There is not a Hydraulic nameplate. It would be 
easy to flip the FDC check valve and flow out thru the FDC siamese connection, 
but not if it will not meet the system demand. My question is, without the 
owner providing what that demand is, how do I know if the 4” FDC method will be 
enough? Or do I remove the 6” elbow and install a tee and some fittings and 
pipe to flow the full 6” out the door which is about 6’ away.