I have done a few of these. I am not sure about 2019, but 2016 main and 
appendix describe how to do this. You are pretty much in the right track
 
 
 
   
 

 
 
>  
> On Apr 13, 2021 at 6:51 PM,  <J H via Sprinklerforum 
> (mailto:sprinklerforum@lists.firesprinkler.org)>  wrote:
>  
>  
>  
>  Any takers? Does anyone retrofit backflows onto pipe scheduled systems? On 
> Mon, Apr 12, 2021 at 2:43 PM J H  <design.azfire...@gmail.com 
> (mailto:design.azfire...@gmail.com)>  wrote:  >  Hello All,  >  We're 
> retrofitting a double check into an existing pipe scheduled system.  >  In 
> looking at NFPA 13 (2019) edition 19.3.2.1 in order to do this we just  >  
> need a hydrant flow test and then subtract the friction losses of the  >  
> double check and the friction loss due to elevation of the highest  >  
> sprinkler from the flow test and make sure the leftover pressure is greater  
> >  than the value of 19.3.2.1. Is that correct?  >   >  JH  >   >  