Are there sprinklers above it? Then they are the calc area.

Do other walls, rated or not, allow the omission with the Density area method?

The sprinklers in the cooler should be treated just like any other room. Unless 
the protection scheme is above.

R/
Matt

-----Original Message-----
From: Sprinklerforum <[email protected]> On Behalf 
Of J H via Sprinklerforum
Sent: Monday, June 14, 2021 4:04 PM
To: [email protected]
Cc: J H <[email protected]>
Subject: Sprinklers in Separate Coolers included in calcs?

Hey Folks,
When dealing with coolers in restaurant kitchen areas do you guys include the 
sprinkler in the cooler in the calculations? I usually do but I'm second 
guessing myself since the cooler does not go up to the ceiling but is it's own 
compartment several feet below ceiling and has overhead protection. I'm 
wondering if the same provision that allows the omission of sprinklers from the 
calcs for obstructions such as ducts would apply?

JH