The details I have seen involve the regular long concrete wedge anchors installed between the hollow cores, in the solid part. I would start by asking the structural engineer and/or hollow core manufacturer how they recommend installing seismic bracing attachments for the sprinkler piping. Welding attachments to the D-Beams may be an option as well (designed by a structural engineer). The regular short drop ins are not an option.
-Skyler On Thu, Jun 17, 2021, 6:43 PM James Crawford via Sprinklerforum < [email protected]> wrote: > We are looking at a project that will be constructed with pre-cast hollow > core concrete panels. > > My concern and question is how do we seismically brace the sprinkler mains > if we can only drill in ¾" into the concrete for the anchor. I know Hilti > has inserts for hanging but not sure if they are OK for seismic bracing. > > Is there anything out there that can be used for seismic bracing of 3", 4" > and 6" mains, if someone can point me in the right direction. > > Thank You > > James Crawford > Phaser Fire Protection Ltd. > Phone 604-888-0318 > Cel: 604-790-0938 > Email [email protected]<mailto:[email protected]> > Web: www.phaserfire.ca<http://www.phaserfire.ca> > > _______________________________________________ > Sprinklerforum mailing list > [email protected] > > http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org > _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org