I have the 1985 book, and it wasn't allowed then.
Same rule as now, ½ x 1 ell to 1" drops.

-----Original Message-----
From: Sprinklerforum <sprinklerforum-boun...@lists.firesprinkler.org> On Behalf 
Of Jennifer Cornett via Sprinklerforum
Sent: Thursday, July 1, 2021 10:45 AM
To: Mark Phillips <philli...@pyebarkerfire.com>; 
Sprinklerforum@lists.firesprinkler.org
Cc: Jennifer Cornett <jcorn...@firetrol.net>
Subject: RE: Sprinkler drop sizing

The branchlines are 1", 1-1/4", etc. with a tee and the drop is ½" pipe to the 
sprinkler heads. Where I would normally design a 1" drop, they used ½".

Sincerely,

Jennifer Cornett, NICET SET
Sprinkler Sales
Firetrol Protection Systems, Inc.
1001 Ave. B
Lubbock, Texas 79401
Ph 806-771-3500
Cell 806-589-9630
Fax 806-771-3501
https://nam02.safelinks.protection.outlook.com/?url=http%3A%2F%2Fwww.firetrol.net%2F&amp;data=04%7C01%7Cdwilson%40blackhawksprinklers.com%7Cae4b0f62c0dc4e334df408d93ca758d7%7C20b3eafa18334148b9c58e75b45c105a%7C1%7C1%7C637607511722507659%7CUnknown%7CTWFpbGZsb3d8eyJWIjoiMC4wLjAwMDAiLCJQIjoiV2luMzIiLCJBTiI6Ik1haWwiLCJXVCI6Mn0%3D%7C2000&amp;sdata=kc%2BlRxn2CSGtMULXo%2FBrodet%2FABlV%2FNbAju5aOPx%2BXM%3D&amp;reserved=0<https://nam02.safelinks.protection.outlook.com/?url=http%3A%2F%2Fwww.firetrol.net%2F&amp;data=04%7C01%7Cdwilson%40blackhawksprinklers.com%7Cae4b0f62c0dc4e334df408d93ca758d7%7C20b3eafa18334148b9c58e75b45c105a%7C1%7C1%7C637607511722507659%7CUnknown%7CTWFpbGZsb3d8eyJWIjoiMC4wLjAwMDAiLCJQIjoiV2luMzIiLCJBTiI6Ik1haWwiLCJXVCI6Mn0%3D%7C2000&amp;sdata=kc%2BlRxn2CSGtMULXo%2FBrodet%2FABlV%2FNbAju5aOPx%2BXM%3D&amp;reserved=0>
____________________________________________________________
This email is intended for the use of the individual or entity to which it is 
addressed and may contain information that is privileged, confidential and 
exempt from disclosure under applicable law.  If the reader of this email 
message is not the intended recipient, or the employee or agent responsible for 
delivery of the message to the intended recipient, you are hereby notified that 
any dissemination, distribution or copying of this communication is prohibited. 
 If you have received this email in error, please notify us immediately by 
telephone at 806-771-3500 and also indicate the sender's name.  Thank you.





From: Mark Phillips <philli...@pyebarkerfire.com>
Sent: Thursday, July 1, 2021 10:39 AM
To: Sprinklerforum@lists.firesprinkler.org
Cc: Jennifer Cornett <jcorn...@firetrol.net>
Subject: Re: Sprinkler drop sizing

Code allows you to retrofit that with a 1/2 x1 ell and a 1 " new drop if the 
outlets are 1/2" off line Could you elaborate?

Sent from my mobile device
Please excuse spelling, grammar, and auto correction.

Mark Phillips
Branch Manager
Fire Sprinkler Design, Install, Inspections Service, Backflows, Fire Alarm 
Inspections

832-101 Purser Drive
Raleigh NC 27603
Phone: 919-779-4010
Fax : 919-779-4014
Cell : 919-268-7587
Email : philli...@pyebarkerfire.com<mailto:philli...@pyebarkerfire.com>
Web : 
https://nam02.safelinks.protection.outlook.com/?url=http%3A%2F%2Fwww.pyebarkerfire.com%2F&amp;data=04%7C01%7Cdwilson%40blackhawksprinklers.com%7Cae4b0f62c0dc4e334df408d93ca758d7%7C20b3eafa18334148b9c58e75b45c105a%7C1%7C1%7C637607511722507659%7CUnknown%7CTWFpbGZsb3d8eyJWIjoiMC4wLjAwMDAiLCJQIjoiV2luMzIiLCJBTiI6Ik1haWwiLCJXVCI6Mn0%3D%7C2000&amp;sdata=8lKepdH2UXH1xGNslAiLJyOv33zmVHpC70aCH3WAsFM%3D&amp;reserved=0<https://nam02.safelinks.protection.outlook.com/?url=https%3A%2F%2Furldefense.com%2Fv3%2F__http%3A%2Fwww.pyebarkerfire.com__%3B!!O7jEn5k3aH8!PWO-uF8HOdKHxZKLsnVXpMFeJLvah-4u_dvJ_LdBhmLV23FhjFlJTFaWWiMVZtspRQ%24&amp;data=04%7C01%7Cdwilson%40blackhawksprinklers.com%7Cae4b0f62c0dc4e334df408d93ca758d7%7C20b3eafa18334148b9c58e75b45c105a%7C1%7C1%7C637607511722517614%7CUnknown%7CTWFpbGZsb3d8eyJWIjoiMC4wLjAwMDAiLCJQIjoiV2luMzIiLCJBTiI6Ik1haWwiLCJXVCI6Mn0%3D%7C2000&amp;sdata=YKJbr7p7a%2FsoZ4THT3ICIuBjpkQav%2BGoLGwBHn8tLXE%3D&amp;reserved=0>

________________________________
From: Sprinklerforum 
<sprinklerforum-boun...@lists.firesprinkler.org<mailto:sprinklerforum-boun...@lists.firesprinkler.org>>
 on behalf of Jennifer Cornett via Sprinklerforum 
<sprinklerforum@lists.firesprinkler.org<mailto:sprinklerforum@lists.firesprinkler.org>>
Sent: Thursday, July 1, 2021 11:31:25 AM
To: 
Sprinklerforum@lists.firesprinkler.org<mailto:Sprinklerforum@lists.firesprinkler.org>
 
<Sprinklerforum@lists.firesprinkler.org<mailto:Sprinklerforum@lists.firesprinkler.org>>
Cc: Jennifer Cornett <jcorn...@firetrol.net<mailto:jcorn...@firetrol.net>>
Subject: Sprinkler drop sizing

[EXTERNAL]

I have a customer with an existing system that the fire marshal wants brought 
up to code. Some is simply adding/relocating heads, but some is that the 
original installation company used 1/2" drops for the sprinkler heads. The fire 
marshal wants all of them changed. The customer wants to know where in code it 
says that 1/2" drops are not acceptable and why using a 1x1/2 reducer is. Thank 
you!

Sincerely,

Jennifer Cornett, NICET SET
Sprinkler Sales
Firetrol Protection Systems, Inc.
1001 Ave. B
Lubbock, Texas 79401
Ph 806-771-3500
Cell 806-589-9630
Fax 806-771-3501
https://nam02.safelinks.protection.outlook.com/?url=http%3A%2F%2Fwww.firetrol.net%2F&amp;data=04%7C01%7Cdwilson%40blackhawksprinklers.com%7Cae4b0f62c0dc4e334df408d93ca758d7%7C20b3eafa18334148b9c58e75b45c105a%7C1%7C1%7C637607511722517614%7CUnknown%7CTWFpbGZsb3d8eyJWIjoiMC4wLjAwMDAiLCJQIjoiV2luMzIiLCJBTiI6Ik1haWwiLCJXVCI6Mn0%3D%7C2000&amp;sdata=EsBFtRTHPrYpXBikh37E8h%2F%2FfpFkMh7FlsfEC7SUhtE%3D&amp;reserved=0<https://nam02.safelinks.protection.outlook.com/?url=http%3A%2F%2Fwww.firetrol.net%2F&amp;data=04%7C01%7Cdwilson%40blackhawksprinklers.com%7Cae4b0f62c0dc4e334df408d93ca758d7%7C20b3eafa18334148b9c58e75b45c105a%7C1%7C1%7C637607511722517614%7CUnknown%7CTWFpbGZsb3d8eyJWIjoiMC4wLjAwMDAiLCJQIjoiV2luMzIiLCJBTiI6Ik1haWwiLCJXVCI6Mn0%3D%7C2000&amp;sdata=EsBFtRTHPrYpXBikh37E8h%2F%2FfpFkMh7FlsfEC7SUhtE%3D&amp;reserved=0>
____________________________________________________________
This email is intended for the use of the individual or entity to which it is 
addressed and may contain information that is privileged, confidential and 
exempt from disclosure under applicable law.  If the reader of this email 
message is not the intended recipient, or the employee or agent responsible for 
delivery of the message to the intended recipient, you are hereby notified that 
any dissemination, distribution or copying of this communication is prohibited. 
 If you have received this email in error, please notify us immediately by 
telephone at 806-771-3500 and also indicate the sender's name.  Thank you.



_______________________________________________
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org<mailto:Sprinklerforum@lists.firesprinkler.org>
https://nam02.safelinks.protection.outlook.com/?url=http%3A%2F%2Flists.firesprinkler.org%2Flistinfo.cgi%2Fsprinklerforum-firesprinkler.org&amp;data=04%7C01%7Cdwilson%40blackhawksprinklers.com%7Cae4b0f62c0dc4e334df408d93ca758d7%7C20b3eafa18334148b9c58e75b45c105a%7C1%7C1%7C637607511722517614%7CUnknown%7CTWFpbGZsb3d8eyJWIjoiMC4wLjAwMDAiLCJQIjoiV2luMzIiLCJBTiI6Ik1haWwiLCJXVCI6Mn0%3D%7C2000&amp;sdata=YF8%2F6MI0A98FHrXybMqGYhM69ln1hnxvqxSv%2BXoJFcU%3D&amp;reserved=0<https://nam02.safelinks.protection.outlook.com/?url=https%3A%2F%2Furldefense.com%2Fv3%2F__http%3A%2Flists.firesprinkler.org%2Flistinfo.cgi%2Fsprinklerforum-firesprinkler.org__%3B!!O7jEn5k3aH8!PWO-uF8HOdKHxZKLsnVXpMFeJLvah-4u_dvJ_LdBhmLV23FhjFlJTFaWWiN8ygl42w%24&amp;data=04%7C01%7Cdwilson%40blackhawksprinklers.com%7Cae4b0f62c0dc4e334df408d93ca758d7%7C20b3eafa18334148b9c58e75b45c105a%7C1%7C1%7C637607511722517614%7CUnknown%7CTWFpbGZsb3d8eyJWIjoiMC4wLjAwMDAiLCJQIjoiV2luMzIiLCJBTiI6Ik1haWwiLCJXVCI6Mn0%3D%7C2000&amp;sdata=F5aGOqNdgVuyk9g%2F5%2BEu1m59f%2BbTOIfvlYfYkGN3r50%3D&amp;reserved=0>
_______________________________________________
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
https://nam02.safelinks.protection.outlook.com/?url=http%3A%2F%2Flists.firesprinkler.org%2Flistinfo.cgi%2Fsprinklerforum-firesprinkler.org&amp;data=04%7C01%7Cdwilson%40blackhawksprinklers.com%7Cae4b0f62c0dc4e334df408d93ca758d7%7C20b3eafa18334148b9c58e75b45c105a%7C1%7C1%7C637607511722517614%7CUnknown%7CTWFpbGZsb3d8eyJWIjoiMC4wLjAwMDAiLCJQIjoiV2luMzIiLCJBTiI6Ik1haWwiLCJXVCI6Mn0%3D%7C2000&amp;sdata=YF8%2F6MI0A98FHrXybMqGYhM69ln1hnxvqxSv%2BXoJFcU%3D&amp;reserved=0