Pete,

You are correct. Where the closet is less than 400 ft3, no clearance is
required below the deflector

Bob Caputo




-----Original Message-----
From: Sprinklerforum <sprinklerforum-boun...@lists.firesprinkler.org> On
Behalf Of Larrimer, Peter A (HEFP\19HEF) via Sprinklerforum
Sent: Thursday, July 1, 2021 10:36 AM
To: sprinklerforum@lists.firesprinkler.org
Cc: Larrimer, Peter A (HEFP\19HEF) <peter.a.larri...@va.gov>
Subject: Closets and Clearance from Deflector to Storage

NFPA 13 (2019 edition) states the following in two sections:

9.5.5.4 Closets. In all closets and compartments, including those closets
housing mechanical equipment, that are not larger than 400 ft3 (11 m3) in
size, a single sprinkler at the highest ceiling level shall be sufficient
without regard to obstructions or minimum distance to the wall.
9.5.6 Clearance from Deflector to Storage.
9.5.6.1* Unless the requirements of 9.5.6.2, 9.5.6.3, 9.5.6.4, or
9.5.6.5 are met, the clearance between the deflector and the top of
storage or contents of the room shall be 18 in. (450 mm) or greater.

Section 9.5.5.4 states "....a single sprinkler at the highest ceiling
level shall be sufficient without regard to obstructions or minimum
distance to the wall."  Does 9.5.5.4 allow a sprinkler to be less than 18
inches from the storage in a closet?  Section 9.5.6.1 does not
specifically say that 9.5.5.4 is an exception to the 18 inch storage
clearance requirement.

However, if the storage less than 18 inches from the deflector is
considered an "obstruction", then it would seem that 9.5.5.4 would allow
storage that is less than 18 inches from the sprinkler deflector in a
closet.

Thanks in advance.

Pete
Dept of VA

_______________________________________________
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.o
rg
_______________________________________________
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to