The prior editions of NFPA 24 do not restrict the use of non-metallic spigot
pieces (riser coming up through the floor from the underground piping)  I
discovered this fact a few years ago, while responding to the question when
doing Advisory Service for NFPA.  I was surprised and concerned for all of
the reasons of exposure now enumerated in the annex when installing
materials this way.

As for temperature, about 8 years ago, I was asked to evaluate a high
pressure problem at a high rise building in Honolulu, where the daily
pressures were excessive. Upon visiting the site, we discovered the
standpipes were interconnected at the top of the building (on the roof) as
opposed to the floor level.  The steel pipe was exposed to direct sunlight
every day...  increasing the system pressure significantly.  We proposed
tenting the pipe on the roof to solve the problem, which it did.

The above is my opinion and has not been processed as a formal
interpretation in accordance with the NFPA Regulations Governing Committee
Projects. This is provided with the understanding that the AFSA assumes no
liability for this opinion or actions taken on it and they are not to be
considered the official position of the AFSA, and/or NFPA or its technical
committees. AFSA cannot provide design or consulting engineering services,
and this opinion should therefore not be considered, nor relied upon, as
such.


Bob Caputo, President
American Fire Sprinkler Association





-----Original Message-----
From: Sprinklerforum <sprinklerforum-boun...@lists.firesprinkler.org> On
Behalf Of Prahl, Craig/GVL via Sprinklerforum
Sent: Tuesday, July 6, 2021 10:47 AM
To: sprinklerforum@lists.firesprinkler.org
Cc: Prahl, Craig/GVL <craig.pr...@jacobs.com>; John Denhardt
<jdenha...@firesprinkler.org>
Subject: RE: [EXTERNAL] Re: Stub-up Material

Thanks for the additional comments John, oh and BTW, I guess the forum
doesn't do different text colors.

My point was that if you are unsure whether or not an item is being used
correctly, go to the sources, either the manufacturer's installation
guidelines, the letter from the recognized testing agency,  or the Approval
Guide and verify one way or another whether the component is being used and
is installed as it was intended.

There are those out there who will try to gain an advantage over others by
substituting cheaper or more easily installed materials regardless of
whether or not the choice material is appropriate or not.   So if it doesn't
seem right, verify.

As far as temperature exposure versus pressure rating degradation, whether
someone agrees or not doesn't matter. It is a tested and proven fact
provided in the published data by the manufacturer.   I'd be curious how the
NFPA 24 committee viewed this information.



Craig Prahl | Jacobs | Group Lead/SME – Fire Protection |
craig.pr...@jacobs.com | www.jacobs.com
1041 East Butler Road   Greenville, South Carolina  29606
CONTACT BY: email or MS TEAMS

-----Original Message-----
From: Sprinklerforum <sprinklerforum-boun...@lists.firesprinkler.org> On
Behalf Of John Denhardt via Sprinklerforum
Sent: Tuesday, July 6, 2021 11:22 AM
To: sprinklerforum@lists.firesprinkler.org
Cc: John Denhardt <jdenha...@firesprinkler.org>
Subject: Re: [EXTERNAL] Re: Stub-up Material

Looking at Craig's comments directly, I want to provide some information.
*(in blue bold)*

1. Go to the manufacturer's data and see if it is listed to be installed
above grade per UL and/or FM as a fire riser. * I am not aware of many
nonmetallic underground materials which are Listed for a fire riser.
The NFPA 24 technical committee acknowledged this during the debates on the
new language which was added for the 2019 editions of NFPA 13 and 24..*

2. Exposure to elevated temperatures such as in a fire event can cause
plastic pipe to fail. The pressure rating of Non-metallic pipe is typically
coupled to the design temperature at which it is intended to be used.  A
class of piping that may be rated for 175 psi at 73 deg. (f) will not
provide the same resiliency at 150 deg (f) and even less at 500 deg. (f).
For example, C900 PVC obtains its pressure rating at an ambient temperature
of 73 deg. (f) at which its pressure rating reduction coefficient would be
100 (100% of pressure rating is attainable).  At 140 deg. (f) it's pressure
reduction coefficient is .22 where it has lost 75% of its pressure rating.
This is why we typically do not accept plastic pipe of any kind above grade
for a riser unless the manufacturer explicitly states that it is Listed
and/or Approved for such an installation. * I do not disagree with the
information.  The NFPA 24 technical committee reviewed this data.*

3. Additional support is needed for the riser assembly.  *Agree.*

*What I want to add is that the NFPA 24 technical committee added new
language in the 2019 editions of NFPA 13 and 24 to cover this application.
This material was discussed and debated in detail.*

NFPA 13 - 6.1.4* Underground piping shall be permitted to extend into

the building through the slab or wall not more than 24 in.

(600 mm). [24:10.1.4]


NFPA 13 - A.6.1.4 Where nonmetallic underground piping is provided

above grade or inside a building, the following should be

considered:

(1) Exposure from direct rays of sunlight

(2) Compatibility with chemicals such as floor coatings and

termiticides/insecticides

(3) Support of piping and appurtenances attached thereto

(e.g., sprinkler risers, backflow preventers)

[24:A.10.1.4]

*I fully understand Craig's concern and as an engineer of record, he can
specify what he wants.  However, the NFPA 24 technical committee understood
these concerns and still allowed the use of this material in this
application.*

*The above is my opinion and has not been processed as a formal
interpretation in accordance with the NFPA Regulations Governing Committee
Projects. This is provided with the understanding that the AFSA assumes no
liability for this opinion or actions taken on it and they are not to be
considered the official position of the **AFSA, and/or NFPA or its technical
committees.**AFSA cannot provide design or consulting engineering services,
and this opinion should therefore not be considered, nor relied upon, as
such.*

Thanks,
John

John August Denhardt, PE
*Vice President, Engineering and Technical Services*

*American Fire Sprinkler Association*
m: p: 301-343-1457
214-349-5965 ext 121
w: firesprinkler.org
<https://urldefense.com/v3/__https://www.facebook.com/firesprinkler.org/__;!!B5cixuoO7ltTeg!TVb4HhVqGQkfYgH1yXI2yMhPH9cH16hP1L-R9uVeY3LqbPxGbKfbNYKU13NKOCu5Ow$
 >
<https://urldefense.com/v3/__https://twitter.com/afsa/status/1039528345367732224__;!!B5cixuoO7ltTeg!TVb4HhVqGQkfYgH1yXI2yMhPH9cH16hP1L-R9uVeY3LqbPxGbKfbNYKU13OIMfnf4w$
 >
<https://urldefense.com/v3/__https://www.linkedin.com/company/american-fire-sprinkler-association-afsa-/__;!!B5cixuoO7ltTeg!TVb4HhVqGQkfYgH1yXI2yMhPH9cH16hP1L-R9uVeY3LqbPxGbKfbNYKU13OjTyt3dw$
 >
   
<https://urldefense.com/v3/__https://www.instagram.com/firesprinklerorg/__;!!B5cixuoO7ltTeg!TVb4HhVqGQkfYgH1yXI2yMhPH9cH16hP1L-R9uVeY3LqbPxGbKfbNYKU13NypVsHYg$
 >

*Our members are at the heart of everything we do.*


*Apprentice Trainers Wanted* It’s time to put your knowledge and experience
to work training the next generation of Fire Sprinkler Fitters and
Technicians. In preparation to deliver related technical instruction (RTI)
for national apprenticeship training, AFSA currently seeks qualified
instructors.  Click here
<https://urldefense.com/v3/__http://www.firesprinkler.org/trainers__;!!B5cixuoO7ltTeg!TVb4HhVqGQkfYgH1yXI2yMhPH9cH16hP1L-R9uVeY3LqbPxGbKfbNYKU13O-0Eqajw$
 > for more information.


On Tue, Jun 29, 2021 at 2:43 PM Prahl, Craig/GVL via Sprinklerforum <
sprinklerforum@lists.firesprinkler.org> wrote:

> I think the question was related to the material, not the height of
> the extension above the slab.
>
> 1. Go to the manufacturer's data and see if it is listed to be
> installed above grade per UL and/or FM as a fire riser.
>
> 2. Exposure to elevated temperatures such as in a fire event can cause
> plastic pipe to fail. The pressure rating of Non-metallic pipe is
> typically coupled to the design temperature at which it is intended to
> be used.  A class of piping that may be rated for 175 psi at 73 deg.
> (f) will not provide the same resiliency at 150 deg (f) and even less at
> 500 deg. (f).
> For example, C900 PVC obtains its pressure rating at an ambient
> temperature of 73 deg. (f) at which its pressure rating reduction
> coefficient would be
> 100 (100% of pressure rating is attainable).  At 140 deg. (f) it's
> pressure reduction coefficient is .22 where it has lost 75% of its
> pressure rating.
> This is why we typically do not accept plastic pipe of any kind above
> grade for a riser unless the manufacturer explicitly states that it is
> Listed and/or Approved for such an installation.
>
> 3. Additional support is needed for the riser assembly.
>
>
>
>
> Craig Prahl | Jacobs | Group Lead/SME – Fire Protection |
> craig.pr...@jacobs.com | http://www.jacobs.com
> 1041 East Butler Road   Greenville, South Carolina  29606
> CONTACT BY: email or MS TEAMS
>
> -----Original Message-----
> From: Sprinklerforum <sprinklerforum-boun...@lists.firesprinkler.org>
> On Behalf Of Ken Wagoner via Sprinklerforum
> Sent: Tuesday, June 29, 2021 1:54 PM
> To: sprinklerforum@lists.firesprinkler.org
> Cc: Ken Wagoner <k...@parsleyconsulting.com>; Jerry Van Kolken <
> jvankol...@mfpc.us>
> Subject: [EXTERNAL] Re: Stub-up Material
>
> Jerry,
> It's in 24
>
> 10.1.4.1* Underground piping shall be permitted to extend into the
> building through the slab or wall not more than 24 in. (600 mm).
>
> See the annex also.  And no California revision to disallow this.
>
> sincerely,
> *Ken Wagoner, SET
> *Parsley Consulting*
> *500 West Mechanic Street
> *Harrisonville, MO 64701
> *****Phone 760-745-6181*
> Visit the website <
> https://urldefense.com/v3/__http://www.parsleyconsulting.com/__;!!B5ci
> xuoO7ltTeg!QsxnsRQTlnie22AZR05QBHGP6Pq1wr5RLmg5SPUE-3J_d0LoRP09tvHM2iN
> Dq5CPxQ$
> > *****
>
>
> **
> On 6/29/2021 10:44 AM, Jerry Van Kolken via Sprinklerforum wrote:
> > I have a project where the UG contractor stub-up with PVC pipe with
> > a
> Mega-lug cap. I've reviewed NFPA 13 / 24 and didn't see anything to
> indicate this was not legit. What / Where can I reference the
> correctness of this installation?
> >
> >
> > Jerry Van Kolken
> > Millennium Fire Protection Corp.
> > 2950 San Luis Rey Rd.
> > Oceanside, CA 92058
> > (760) 722-2722 FX 722-2730
> >
> > CONFIDENTIALITY NOTICE This e-mail and any attachments are for the
> > sole
> use of the intended recipients and contain information that may be
> confidential or legally privileged. If you have received this e-mail
> in error, please notify the sender by reply e-mail and delete the
> message. Any disclosure, copying, distribution, or use of this
> communication by someone other than the intended recipient is prohibited.
> > _______________________________________________
> > Sprinklerforum mailing list
> > Sprinklerforum@lists.firesprinkler.org
> > https://urldefense.com/v3/__http://lists.firesprinkler.org/listinfo.
> > cg
> > i/sprinklerforum-firesprinkler.org__;!!B5cixuoO7ltTeg!QsxnsRQTlnie22
> > AZ R05QBHGP6Pq1wr5RLmg5SPUE-3J_d0LoRP09tvHM2iPn9bOwbg$
>
> _______________________________________________
> Sprinklerforum mailing list
> Sprinklerforum@lists.firesprinkler.org
>
> https://urldefense.com/v3/__http://lists.firesprinkler.org/listinfo.cg
> i/sprinklerforum-firesprinkler.org__;!!B5cixuoO7ltTeg!QsxnsRQTlnie22AZ
> R05QBHGP6Pq1wr5RLmg5SPUE-3J_d0LoRP09tvHM2iPn9bOwbg$
>
> ________________________________
>
> NOTICE - This communication may contain confidential and privileged
> information that is for the sole use of the intended recipient. Any
> viewing, copying or distribution of, or reliance on this message by
> unintended recipients is strictly prohibited. If you have received
> this message in error, please notify us immediately by replying to the
> message and deleting it from your computer.
> _______________________________________________
> Sprinklerforum mailing list
> Sprinklerforum@lists.firesprinkler.org
>
> https://urldefense.com/v3/__http://lists.firesprinkler.org/listinfo.cg
> i/sprinklerforum-firesprinkler.org__;!!B5cixuoO7ltTeg!TVb4HhVqGQkfYgH1
> yXI2yMhPH9cH16hP1L-R9uVeY3LqbPxGbKfbNYKU13OJhu0ecA$
>
_______________________________________________
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
https://urldefense.com/v3/__http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org__;!!B5cixuoO7ltTeg!TVb4HhVqGQkfYgH1yXI2yMhPH9cH16hP1L-R9uVeY3LqbPxGbKfbNYKU13OJhu0ecA$

________________________________

NOTICE - This communication may contain confidential and privileged
information that is for the sole use of the intended recipient. Any viewing,
copying or distribution of, or reliance on this message by unintended
recipients is strictly prohibited. If you have received this message in
error, please notify us immediately by replying to the message and deleting
it from your computer.
_______________________________________________
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org