Totally my opinion and worth every penny you're paying for it, if the purpose of closing the dampers is to maintain volumetric integrity of the compartment vis-a-vis the amount of agent I would consider that function to be art of the suppression system and so controlled by the releasing panel. If on the other hand closing the dampers is to prevent smoke migration to other areas of the building I'd consider itb to be part of the building fore alarm system and so controlled by the FAP. Just thinking out loud.
On Mon, Aug 23, 2021 at 3:00 PM James Crawford via Sprinklerforum < sprinklerforum@lists.firesprinkler.org> wrote: > NFPA 2001 (2018) > > We have a clean agent system that is protecting a server room, we have > gone in to do the electrical connections and the base building electricians > have connected the ventilation dampers to the base building alarm panel > > My understanding is that they should be connected to the release panel for > the clean agent system as this is how we have always done this. > > I have always based it on section 4.3.1.1.4 The clean agent suppression > system release control panel shall not be dependent or affected by the > operation or failure of the protected premises building fire alarm panel. > > Am I missing something or is this allowed, as I cannot find anything else > that say otherwise. > > Thank You > > James Crawford > Phaser Fire Protection Ltd. > Phone 604-888-0318 > Cel: 604-790-0938 > Email jcrawf...@phaserfire.ca<mailto:jcrawf...@phaserfire.ca> > Web: www.phaserfire.ca<http://www.phaserfire.ca> > > _______________________________________________ > Sprinklerforum mailing list > Sprinklerforum@lists.firesprinkler.org > > http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org > _______________________________________________ Sprinklerforum mailing list Sprinklerforum@lists.firesprinkler.org http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org