NFPA 13 (13ed) section 8.11.5
Is it just me or do these rules seem even more restrictive that ESFR? There also appears to be some gaps on how to treat certain obstructions. Here are some of the areas I need some clarification from the forum onβ¦.. 8.11.5.2- How do you treat an obstruction >8in but <24in in width with the bottom of the obstruction located within 24in of the sprinkler deflector? 8.11.5.3.2-. Does this table mean that if my deflector is greater than 6in above the obstruction bottom the sprinkler must be located at lease 36β away from the edge of the obstruction? 8.11.5.3.4 β apply this for obstructions located >24in below the deflector unless they fall under 8.15.5.2.1.3 8.11.5.3.5 β Does this section supersede the requirements of 8.11.5.2.1.3 and 8.11.5.3.4 for anything running parallel to the branch lines? Thank you, Dewayne Martinez _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org