I agree with you, but the manual wet is full of water and leakage could be 
detected same as a dry automatic, but you have to test the wet manual.  I would 
think the air and water mixture of a dry automatic would lead to corrosion 
problems faster than a manual wet.  Especially since dry pipe valves need to be 
tripped every year and you are introducing water at that point.  Evan a partial 
trip will leave some condensation in addition to whatever moisture you get from 
the air compressor. At this time we don't hydrotest dry automatic standpipes, 
but the question came up as to why.  Thanks.

Jay Stough 
NICET IV LAYOUT 
NICET III ITM 

    On Thursday, October 28, 2021, 02:25:14 PM EDT, Mike Morey 
<[email protected]> wrote:  
 
 The hydro is to find out if the thing is full of holes IIRC.  Automatic dry 
has air pressure to monitor that, the others don't.  Presumably this will be 
updated when all standpipes have to be air supervised for leakage (in the next 
edition, as of now, of 14)

Mike Morey
CFPS 3229 • NICET S.E.T. 123677
Project Manager • Fire Protection Group
Shambaugh & Son, LP an EMCOR Company
7614 Opportunity Drive • Fort Wayne, IN • 46825
direct 260.487.7824 /  cell 260.417.0625 /  fax 260.487.7991
email [email protected]



-----Original Message-----
From: Sprinklerforum <[email protected]> On Behalf 
Of jaycs7919--- via Sprinklerforum
Sent: Thursday, October 28, 2021 2:19 PM
To: Sprinkler Forum <[email protected]>
Cc: [email protected]
Subject: Hydrostatic testing of Automatic Dry Standpipes

 
BE ADVISED - This email originated outside EMCOR. 
 

Do you have to do a hydrostatic test of an automatic dry standpipe based on the 
2017 or 2020 edition of 25?  
https://urldefense.com/v3/__http://6.3.2.1__;!!FaxH778!JXv4ug48P204AzhXwW0J9xcK7hgbtEeaK5RFdEz1iPXJcmBcCujziJZbsNmvcaLL$
  calls out the hydrostatic test of manual stadpipes and semiautomatic dry 
standpipes; no mention of automatic dry standpipes.  Under the definitions, the 
difference is that the semiautomatic uses a deluge valve with pull stations or 
some control device to activate the system.  The automatic uses a dry valve and 
opening the valve operates the system.  It doesn't make sense that you would 
test one type but not the other.  What am I missing?

Jay Stough 
NICET IV LAYOUT 
NICET III ITM
_______________________________________________
Sprinklerforum mailing list
[email protected]
https://urldefense.com/v3/__http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org__;!!FaxH778!JXv4ug48P204AzhXwW0J9xcK7hgbtEeaK5RFdEz1iPXJcmBcCujziJZbsC2IrYI-$
 

This message is for the named person's use only.  It may contain confidential, 
proprietary or legally privileged information. No confidentiality or privilege 
is waived or lost by any mistransmission.  If you receive this message in 
error, please  immediately delete it and all copies of it from your system, 
destroy any hard copies of it and notify the sender.  You must not, directly or 
indirectly, use, disclose, distribute, print, or copy any part of this message 
if you are not the intended recipient.
  
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to