The architect has it backwards. The contract documents are where it needs to be 
in writing that the fire sprinkler protection system must be designed and 
installed in a specific manner. That specific manner must be explicitly stated 
in the fire protection documents or be the unambiguous conclusion of the 
document’s interpretation by an experienced fire protection contractor of 
reasonable intelligence. If the specific design manner is somehow present in 
documents excluded from the fire protection contractor, like sometimes happens 
for any number of reasons, then the general contractor has a tit in the 
wringer. You as contractor might be happy to volunteer ideas as to what color 
the architect is going to paint the fire protection system components.

Allan Seidel
St. Louis, MO

> On Nov 8, 2021, at 9:21 AM, Brian Harris via Sprinklerforum 
> <sprinklerforum@lists.firesprinkler.org> wrote:
> 
> I know it's common practice to run Mains parallel with the structure and 
> Branchlines perpendicular to it but is that written anywhere? I actually have 
> an architect that would like to see it in writing...
> 
> Brian Harris, CET
> BVS Systems Inc.
> Design Manager
> bvssystemsinc.com<http://bvssystemsinc.com/>
> Phone: 704.896.9989
> Fax: 704.896.1935
> 