Thank you for the responses I received. Based on this information I have asked the Architect to review once more his review. BTW the 2020 NYSBC codes are the documents being used.
Regards, G. Tim Stone G. Tim Stone Consulting, LLC NICET Level III Engineering Technician Fire Protection Sprinkler Design and Consulting Services 117 Old Stage Rd. - Essex Jct., VT. 05452 CELL: (802) 373-0638 TEL: (802) 434-2968 tston...@comcast.net -----Original Message----- From: Sprinklerforum <sprinklerforum-boun...@lists.firesprinkler.org> On Behalf Of Steve Leyton via Sprinklerforum Sent: Tuesday, November 9, 2021 4:36 PM To: sprinklerforum@lists.firesprinkler.org Cc: Steve Leyton <st...@protectiondesign.com>; Salvatore Izzo <sizzo...@gmail.com> Subject: RE: 13R Installation of Sprinkler Systems in Low-Rise Residential Occupancies Good call Sal; as I said in my response, it's up to the Building Official to clarify whether that separation has to be two or three hours. But a solid concrete slab makes that a fairly easy exercise and the only upgrades would be the ratings of fire stops because shafts for utilities and stairs will be what they will be based on the construction type and FR rating. Steve Leyton, President Protection Design and Consulting T | 619.255.8964 x 102 | www.protectiondesign.com 2851 Camino Del Rio South | Suite 210 | San Diego, CA 92108 Fire Protection System Design | Consulting | Planning | Training -----Original Message----- From: Sprinklerforum <sprinklerforum-boun...@lists.firesprinkler.org> On Behalf Of Salvatore Izzo via Sprinklerforum Sent: Tuesday, November 09, 2021 1:29 PM To: sprinklerforum@lists.firesprinkler.org Cc: Salvatore Izzo <sizzo...@gmail.com> Subject: Re: 13R Installation of Sprinkler Systems in Low-Rise Residential Occupancies Hope all is well with everyone. Building codes are typically very clear on what characterizes a building to be separate and distinct. Either build a building by itself, build multiple buildings and separate by fire separation distance is specified by the code, build two buildings right smack up against each other and separate by an approved or listed firewall assembly, or use the special provision in the IBC that applies typically to what we call podium-style buildings. Section 510.2 of the 2018 IBC requires a horizontal assembly having a fire resistance rating of not less than three hours for a single building to be considered as separate and distinct buildings. A 2-hour fire separation assembly effectively serves to separate fire areas, but, in my opinion, it would not qualify a single structure to be considered as separate and distinct buildings recognized by the building code. Rather, it would be categorized as a mixed occupancy, requiring NFPA 13 sprinkler protection throughout. Am I missing something? On Tue, Nov 9, 2021 at 3:55 PM tstone52--- via Sprinklerforum < sprinklerforum@lists.firesprinkler.org> wrote: > Steve, > That is exactly what the Architect that I am working for told me. The > two hour Horizontal separation between the floors make this 2 separate > buildings. > > Thank you. > > Regards, > G. Tim Stone > > G. Tim Stone Consulting, LLC > NICET Level III Engineering Technician Fire Protection Sprinkler > Design and Consulting Services > > 117 Old Stage Rd. - Essex Jct., VT. 05452 > <https://www.google.com/maps/search/117+Old+Stage+Rd.+-+Essex+Jct.,+VT.+0545 2?entry=gmail&source=g> > CELL: (802) 373-0638 TEL: (802) 434-2968 > tston...@comcast.net > > -----Original Message----- > From: Steve Leyton <st...@protectiondesign.com> > Sent: Tuesday, November 9, 2021 3:51 PM > To: sprinklerforum@lists.firesprinkler.org > Cc: tston...@comcast.net > Subject: RE: 13R Installation of Sprinkler Systems in Low-Rise > Residential Occupancies > > Assuming the building code that's applicable to this project > classifies this as two separate buildings (a four-story Type 3 on a > single-story Type 1 podium), NFPA 13R can be used as a basis of design > in many (most?) > jurisdictions. It is up to the building official to clarify whether a > two- > or three-hour separation is required between the podium and upper > floors, but this is commonly viewed as two separate buildings. > > I have served as member of the NFPA Technical Committee for > Residential Sprinklers, but this is MY opinion only. > > > Steve Leyton, President > Protection Design and Consulting > T | 619.255.8964 x 102 | www.protectiondesign.com > 2851 Camino Del Rio South | Suite 210 | San Diego, CA 92108 Fire > Protection System Design | Consulting | Planning | Training > > > > > -----Original Message----- > From: Sprinklerforum <sprinklerforum-boun...@lists.firesprinkler.org> > On Behalf Of tstone52--- via Sprinklerforum > Sent: Tuesday, November 09, 2021 12:42 PM > To: sprinklerforum@lists.firesprinkler.org > Cc: tston...@comcast.net > Subject: 13R Installation of Sprinkler Systems in Low-Rise Residential > Occupancies > > Am I reading the Scope of 13R correctly? > > > > I am designing a Sprinkler system for a building which is five stories > in height. Each floor is about 5,500 SF. The Ground floor is a parking > garage of concrete & steel (Type 1a construction) with 4 stories of > Residential above which constructed of wood (Type 3B Construction). > The parking garage shall be protected by a Dry Pipe System designed in > accordance with NFPA 13. > There is a 2 hour Occupancy Separation between Garage & The Second Floor. > The Second thru Fifth levels are to be protected by a NFPA 13R > Sprinkler System. The overall building height measures less than 60' above grade. > > > > NFPA 13R Scope: states this standard shall cover ____ "residential > occupancies up to and including four stories in height in buildings > not exceeding 60 ft. in height above grade plane." > > > > Due to the phrase "in Buildings" am I interpreting this correctly? > > > > Regards, > > G. Tim Stone > > > > G. Tim Stone Consulting, LLC > > NICET Level III Engineering Technician > > Fire Protection Sprinkler Design > > and Consulting Services > > > > 117 Old Stage Rd. - Essex Jct., VT. 05452 > <https://www.google.com/maps/search/117+Old+Stage+Rd.+-+Essex+Jct.,+VT > .+05452?entry=gmail&source=g> > > CELL: (802) 373-0638 TEL: (802) 434-2968 > > <mailto:tston...@comcast.net> tston...@comcast.net > > > > _______________________________________________ > Sprinklerforum mailing list > Sprinklerforum@lists.firesprinkler.org > > http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl > er.org > > _______________________________________________ > Sprinklerforum mailing list > Sprinklerforum@lists.firesprinkler.org > > http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl > er.org > _______________________________________________ Sprinklerforum mailing list Sprinklerforum@lists.firesprinkler.org http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org _______________________________________________ Sprinklerforum mailing list Sprinklerforum@lists.firesprinkler.org http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org _______________________________________________ Sprinklerforum mailing list Sprinklerforum@lists.firesprinkler.org http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org