Yes, I have done an FM approved ESFR job with beams spaced 5'-0" o.c., and only 
calc'd. for 12 heads.
Also baffles are not allowed with ESFR sprinklers.

Dennis Wilson
Blackhawk Sprinklers.


-----Original Message-----
From: Sprinklerforum <sprinklerforum-boun...@lists.firesprinkler.org> On Behalf 
Of Kyle.Montgomery via Sprinklerforum
Sent: Wednesday, December 29, 2021 2:10 PM
To: sprinklerforum@lists.firesprinkler.org
Cc: Kyle.Montgomery <kmontgom...@aerofire.com>; Mike Hairfield <fsl...@msn.com>
Subject: RE: ESFR - Minimum Remote Area Size

In the FM Datasheets, it looks like the minimum design area is 768 sq ft (64 x 
12), EXCEPT when sprinklers are required in every channel created by obstructed 
construction. In the case of sprinklers in every channel, it appears as though 
you just calculate the required minimum number of sprinklers. I THINK 
(certainly not a leading authority on this) that the heat from a fire will be 
directed along the channel, which minimizes the concern for "skipping".

Anyone else have thoughts on this, either in agreement or otherwise? 

It looks like I can protect it per FM Global criteria, but I'd rather not open 
that can of worms if there's a legitimate way to apply NFPA 13. I guess it all 
comes down to whether the minimum spacing applies if there is a solid 
obstruction between the sprinklers. I'm confident that it wouldn't with 
standard spray sprinklers, but looking for some reassurance (or rebuke) when it 
comes to ESFR.

-Kyle M

-----Original Message-----
From: Sprinklerforum <sprinklerforum-boun...@lists.firesprinkler.org> On Behalf 
Of Kyle.Montgomery via Sprinklerforum
Sent: Wednesday, December 29, 2021 12:41 PM
To: sprinklerforum@lists.firesprinkler.org
Cc: Kyle.Montgomery <kmontgom...@aerofire.com>; Mike Hairfield <fsl...@msn.com>
Subject: [EXTERNAL] RE: ESFR - Minimum Remote Area Size

Deflector distance isn't a problem, I can either run the branch line up high in 
every pocket/bay or utilize an upright ESFR (Tyco ESFR-17).

I was thinking that the minimum spacing didn't apply when there was an 
obstruction/baffle between the heads (in this case, the legs of the concrete 
tee) and the heads are installed in "every bay channel formed by solid 
structural members". This is specifically allowed in the FM Datasheets, but I 
believe they also have a minimum remote areas size that would require you to 
add sprinklers to the remote area. 

Is the consensus among the group that this building (concrete tees with legs 5 
feet on center) just cannot be protected with ESFR sprinklers per NFPA 13?

And, if that's the case, are we also saying that any time there is a 
beam/obstruction in an ESFR system that the heads on either side of it still 
need to be at least 8 feet apart? You can't have a head 3 feet away on each 
side of the beam (heads 6 feet apart but with a solid obstruction/baffle 
between them)?

-Kyle M

-----Original Message-----
From: Sprinklerforum <sprinklerforum-boun...@lists.firesprinkler.org> On Behalf 
Of Mike Hairfield via Sprinklerforum
Sent: Wednesday, December 29, 2021 12:22 PM
To: sprinklerforum@lists.firesprinkler.org
Cc: Mike Hairfield <fsl...@msn.com>
Subject: [EXTERNAL] Re: ESFR - Minimum Remote Area Size

I don’t believe ESFR sprinklers can be installed in a concrete tee building.
Minimum spacing is 8’-0” and what is the deflector distance.
Mike 

Sent from my iPhone

> On Dec 29, 2021, at 2:11 PM, Kyle.Montgomery via Sprinklerforum 
> <sprinklerforum@lists.firesprinkler.org> wrote:
> 
> I'm dealing with an existing concrete tee building that the owner wants to 
> retrofit with an ESFR system. Heads will be closely spaced due to the 
> obstruction caused by the tees; 5-foot on center. Does NFPA 13 have a minimum 
> remote area size, or is it just 12 heads?
> 
> -Kyle M
> 
> _______________________________________________
> Sprinklerforum mailing list
> Sprinklerforum@lists.firesprinkler.org
> https://nam02.safelinks.protection.outlook.com/?url=https%3A%2F%2Furldefense.com%2Fv3%2F__https%3A%2F%2Fna01.safelinks.protection.outlook.com%2F%3Furl%3Dhttp*3A*2F*2Flists.firesprinkler.org*2Flistinfo.cgi*2Fsprinklerforum-firesprinkler.org%26amp%3Bdata%3D04*7C01*7C*7C2243e8f422f447e9e98808d9caff0ba5*7C84df9e7fe9f640afb435aaaaaaaaaaaa*7C1*7C0*7C637764019046194532*7CUnknown*7CTWFpbGZsb3d8eyJWIjoiMC4wLjAwMDAiLCJQIjoiV2luMzIiLCJBTiI6Ik1haWwiLCJXVCI6Mn0*3D*7C3000%26amp%3Bsdata%3Dpbf*2BoThaf77nppLZONRpZrs9AwSkwAHo*2FPdId21LXD8*3D%26amp%3Breserved%3D0__%3BJSUlJSUlJSUlJSUlJSUlJSUlJQ!!Ba8_KKAT!cFpuCO_w9YY4Ug5JApVoeXhH0dAjA9mRe1AyvYgW_8Szjt_tnI_096ZtrSXQJ6oSgXY%24&amp;data=04%7C01%7Cdwilson%40blackhawksprinklers.com%7C5c7f1931d0954dba539a08d9cb07297c%7C20b3eafa18334148b9c58e75b45c105a%7C1%7C1%7C637764053907638885%7CUnknown%7CTWFpbGZsb3d8eyJWIjoiMC4wLjAwMDAiLCJQIjoiV2luMzIiLCJBTiI6Ik1haWwiLCJXVCI6Mn0%3D%7C3000&amp;sdata=FrmpU9%2FEGhRmnuPsunYJ38%2BaVWftRIWjQ0Z%2FBtRlnDc%3D&amp;reserved=0
>  
_______________________________________________
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
https://nam02.safelinks.protection.outlook.com/?url=https%3A%2F%2Furldefense.com%2Fv3%2F__http%3A%2F%2Flists.firesprinkler.org%2Flistinfo.cgi%2Fsprinklerforum-firesprinkler.org__%3B!!Ba8_KKAT!cFpuCO_w9YY4Ug5JApVoeXhH0dAjA9mRe1AyvYgW_8Szjt_tnI_096ZtrSXQNV76eoU%24&amp;data=04%7C01%7Cdwilson%40blackhawksprinklers.com%7C5c7f1931d0954dba539a08d9cb07297c%7C20b3eafa18334148b9c58e75b45c105a%7C1%7C1%7C637764053907638885%7CUnknown%7CTWFpbGZsb3d8eyJWIjoiMC4wLjAwMDAiLCJQIjoiV2luMzIiLCJBTiI6Ik1haWwiLCJXVCI6Mn0%3D%7C3000&amp;sdata=rnp1V43GlcN%2BGBSardVXa8JZOo1g0oku5GtATtS3MOU%3D&amp;reserved=0
 
_______________________________________________
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
https://nam02.safelinks.protection.outlook.com/?url=https%3A%2F%2Furldefense.com%2Fv3%2F__http%3A%2F%2Flists.firesprinkler.org%2Flistinfo.cgi%2Fsprinklerforum-firesprinkler.org__%3B!!Ba8_KKAT!YTVAuSzdiMYPwqZfcNAGOrGotgsI64o1BjqnawO_wJ_H_lOjDSSwHAUJxZFtTaUFcBg%24&amp;data=04%7C01%7Cdwilson%40blackhawksprinklers.com%7C5c7f1931d0954dba539a08d9cb07297c%7C20b3eafa18334148b9c58e75b45c105a%7C1%7C1%7C637764053907638885%7CUnknown%7CTWFpbGZsb3d8eyJWIjoiMC4wLjAwMDAiLCJQIjoiV2luMzIiLCJBTiI6Ik1haWwiLCJXVCI6Mn0%3D%7C3000&amp;sdata=pPNLcXFubVq76EOe0JxRd5j1BplHJoturwxV0CLOszg%3D&amp;reserved=0
 
_______________________________________________
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
https://nam02.safelinks.protection.outlook.com/?url=http%3A%2F%2Flists.firesprinkler.org%2Flistinfo.cgi%2Fsprinklerforum-firesprinkler.org&amp;data=04%7C01%7Cdwilson%40blackhawksprinklers.com%7C5c7f1931d0954dba539a08d9cb07297c%7C20b3eafa18334148b9c58e75b45c105a%7C1%7C1%7C637764053907638885%7CUnknown%7CTWFpbGZsb3d8eyJWIjoiMC4wLjAwMDAiLCJQIjoiV2luMzIiLCJBTiI6Ik1haWwiLCJXVCI6Mn0%3D%7C3000&amp;sdata=1zhLMNRBFPg7OBL7Btu40G5Q6Nm%2BWNSYmgtKLemrThQ%3D&amp;reserved=0
_______________________________________________
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to