I remember from my AFSA (Old School) design training course, that threads and 
engagements are tapered.

3 exposed  is set as a nominal number. For 1" pipe, the actual number left 
showing is 2 7/8.-ish

It is based on threads per inch, along a taper.

Reference the ASTM standards for exact numbers.

R/
Matt

-----Original Message-----
From: Sprinklerforum <sprinklerforum-boun...@lists.firesprinkler.org> On Behalf 
Of Matt Grise via Sprinklerforum
Sent: Wednesday, January 5, 2022 7:42 AM
To: sprinklerforum@lists.firesprinkler.org
Cc: Matt Grise <m...@afpsprink.com>; Kevin Hall <kh...@firesprinkler.org>
Subject: RE: Thread connection holding on one thread only

If I recall from my book-learning days, there is a pretty well established 
minimum thread engagement that provides the full strength of a threaded 
connection. (maybe 3?). That may also only apply to bolts though.

Matt 


-----Original Message-----
From: Sprinklerforum <sprinklerforum-boun...@lists.firesprinkler.org> On Behalf 
Of Kevin Hall via Sprinklerforum
Sent: Wednesday, January 05, 2022 8:33 AM
To: sprinklerforum@lists.firesprinkler.org
Cc: Kevin Hall <kh...@firesprinkler.org>
Subject: Re: Thread connection holding on one thread only

I do not believe one is sufficient. I recall a project where the specification 
limited the maximum number of exposed threads to 2 or 3. I'd have to do some 
research to find the product/installation standard that was referenced.


Kevin Hall, M.Eng., P.E., ET, CWBSP, PMSFPE

Coordinator, Engineering and Technical Services

American Fire Sprinkler Association

kh...@firesprinkler.org

214-349-5971


On Wed, Jan 5, 2022 at 2:16 AM Dan Arbel via Sprinklerforum < 
sprinklerforum@lists.firesprinkler.org> wrote:

> Dear Forum Members
>
> I have a case where 1.25" NPT pipe nipple was connected to 1.25" BSP 
> (as per British standard) pipe.
>
> Sprinkler System in interstitial space.
>
> There was only 2 threads engagement.
>
> After about 15 years somebody touched the a pipe and the connection 
> disengaged.
>
> I would appreciated the members opinion on the allegation that even 
> one thread engagement is sufficient providing sufficient strength.
>
> Dan Arbel
> Dan Arbel Risk Engineering Ltd
> Mail: d...@riskmanage.com
> WEB SITE: 
> https://linkprotect.cudasvc.com/url?a=https%3a%2f%2fwww.riskmanage.com
> &c=E,1,rOBCJWaUiWX-Zi-j03j48v-ojODJ4zDjCTCn-XcTQUWSVSZzQRanv2vrdqlUogX
> nkOECEYOqMT2eMuzN6PVEfyuVyVF6Hoz4BiV1VyGvBRCcljgZH2U,&typo=1
> Mobile: +972-52-6611337
> Tel: +972-4-8243337
> _______________________________________________
> Sprinklerforum mailing list
> Sprinklerforum@lists.firesprinkler.org
>
> https://linkprotect.cudasvc.com/url?a=http%3a%2f%2flists.firesprinkler
> .org%2flistinfo.cgi%2fsprinklerforum-firesprinkler.org&c=E,1,RvPpy3ldS
> C8kzu280ouAOq2QKBzNGfMu7REiocN-XOdCtouKzXB4EaUtnbHa1UoPns-R2H1fzQj-fW-
> oIX3YW0Doh9ZL84fg3cNaQ0q1OQ,,&typo=1
>
_______________________________________________
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
https://linkprotect.cudasvc.com/url?a=http%3a%2f%2flists.firesprinkler.org%2flistinfo.cgi%2fsprinklerforum-firesprinkler.org&c=E,1,wikZY07kLJSV87o86Ivs1Jsxm4l75jKdQbbfbZ7tVZifvQRGY33Wh20_IAQ7wACFTF9yFLpxM-xqELTjxDST6UJ7dCl0WTqJP_LkvfP8qA,,&typo=1
_______________________________________________
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

_______________________________________________
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to