My question is: Are QR uprights listed to be used in those areas or does it
have to be a CCS sprinkler?

Troy

-----Original Message-----
From: Sprinklerforum <sprinklerforum-boun...@lists.firesprinkler.org> On
Behalf Of Tom Wellen via Sprinklerforum
Sent: January 11, 2022 3:56 PM
To: sprinklerforum@lists.firesprinkler.org
Cc: Tom Wellen <tgwel...@gmail.com>; Trillium Fire Sprinkler Design INC
<trilliumf...@cwisp.ca>
Subject: Re: COMBUSTIBLE CONCEALED SPACE

Troy,

No. NFPA 13, 2019 edition in 9.3.2 is specific that sprinklers are listed
for horizontal combustible concealed spaces. Specifically listed to provide
protection.....




On Tue, Jan 11, 2022 at 2:40 PM Trillium Fire Sprinkler Design INC via
Sprinklerforum <sprinklerforum@lists.firesprinkler.org> wrote:

> Can someone confirm that it is not mandatory to use CCS sprinklers in 
> a space 36" or less?
>
>
>
> I know it allows for larger spacing, but code wise. I don't believe 
> they are a must and the space can be protected with QR uprights.
>
>
>
> Regards
>
>
>
> Troy S
>
> _______________________________________________
> Sprinklerforum mailing list
> Sprinklerforum@lists.firesprinkler.org
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
> er.org
>


--
Tom Wellen - May '91
Senior Fire Protection Consultant
Fire Engineering & Consulting, LLC
(972) 355-2159
fireeac.com

<http://fireeac.com/>
_______________________________________________
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

_______________________________________________
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to