The liquid is a corrosive, non-issue from our perspective.

I would wager they don't have adequate secondary containment or spill control 
within the room where these are stored which is why they're using these IBC 
containment units.

I'd be curious how many totes do they store in this area?  If the number is 
small, is there another room where they can be stored, possibly one that could 
be provided with the proper secondary containment whereby allowing the totes to 
be placed on the slab or one that could be protected properly but less costly 
being of a smaller footprint?

Craig Prahl | Jacobs | Group Lead/SME - Fire Protection | 
craig.pr...@jacobs.com | www.jacobs.com
1041 East Butler Road   Greenville, South Carolina  29606
CONTACT BY: email or MS TEAMS



-----Original Message-----
From: Steve Mackinnon <ste...@hartcorn.com>
Sent: Wednesday, January 26, 2022 3:16 PM
To: Prahl, Craig/GVL <craig.pr...@jacobs.com>; 
sprinklerforum@lists.firesprinkler.org
Cc: Art Tiroly <atir...@atcofirepro.com>
Subject: [EXTERNAL] RE: question about Storage height

I'm not sure if attachments are allowed, if yes this is the situation...

I believe the liquid is classified as a low commodity, leaving the plastic 
containers as the driving force... ok, I'm on board with this.

We are trying to reduce the overall plastic height or commodity 
classification... a Group A plastic upgrade at 10 feet is costing them six 
figures in FS upgrades (new underground, fire pump etc).

-----Original Message-----
From: Prahl, Craig/GVL <craig.pr...@jacobs.com>
Sent: Wednesday, January 26, 2022 2:53 PM
To: sprinklerforum@lists.firesprinkler.org
Cc: Steve Mackinnon <ste...@hartcorn.com>; Art Tiroly <atir...@atcofirepro.com>
Subject: RE: question about Storage height

You don't have 5 ft of commodity.  The liquid within the tote is irrelevant to 
the hazard.  You essentially have a plastic hazard that is 10 ft in height.  
Now, there are some schools of thought that derate the level of hazard due to 
the liquid acting as a heat sink and thereby providing a reduced potential for 
fire involvement when compared to that of the empty totes.  But, since there 
are empty as well as full and possibly partially full totes, it would be safer 
to assume the hazard as a Group A plastic at 10 ft in height and move on.

Craig Prahl | Jacobs | Group Lead/SME - Fire Protection | 
craig.pr...@jacobs.com | www.jacobs.com
1041 East Butler Road   Greenville, South Carolina  29606
CONTACT BY: email or MS TEAMS



-----Original Message-----
From: Sprinklerforum <sprinklerforum-boun...@lists.firesprinkler.org> On Behalf 
Of Steve Mackinnon via Sprinklerforum
Sent: Wednesday, January 26, 2022 1:46 PM
To: sprinklerforum@lists.firesprinkler.org
Cc: Steve Mackinnon <ste...@hartcorn.com>; Art Tiroly <atir...@atcofirepro.com>
Subject: [EXTERNAL] RE: question about Storage height

Thank you everyone who replied, it appears it's not as clear cut as one would 
think lol.

The plastic tote below does have a solid top, but I would assume there would be 
opening in the cover to allow any spillage or leaks to fall into the vessel. 
And allow any sprinkler water to fill the totes... but again, these are one 
time usage only.

Not sure if it helps, but there are only 3-5 of these in the warehouse...

I just find it hard to wrap my head around protecting 10 foot of storage for 
only 5 feet of commodity.

Thank you again!

-----Original Message-----
From: Sprinklerforum <sprinklerforum-boun...@lists.firesprinkler.org> On Behalf 
Of Art Tiroly via Sprinklerforum
Sent: Wednesday, January 26, 2022 1:35 PM
To: sprinklerforum@lists.firesprinkler.org
Cc: Art Tiroly <atir...@atcofirepro.com>
Subject: RE: question about Storage height

Is the spill container open top? That will be an issue. These sound like 
plastic totes. If the liquid is not combustible the empty tote is still a lot 
of plastic

Art

-----Original Message-----
From: Sprinklerforum <sprinklerforum-boun...@lists.firesprinkler.org> On Behalf 
Of Scott Futrell via Sprinklerforum
Sent: Wednesday, January 26, 2022 9:32 AM
To: sprinklerforum@lists.firesprinkler.org
Cc: Scott Futrell <sco...@ffcdi.com>; Mike Hairfield <fsl...@msn.com>
Subject: RE: question about Storage height

You didn't mention what the liquid is. If it is a hazardous material as 
recognized by the International Fire Code then the 'empty' container is still 
considered full unless completely cleaned.

Scott

Office: (763) 425-1001 x 2
Cell: (612) 759-5556

-----Original Message-----
From: Sprinklerforum <sprinklerforum-boun...@lists.firesprinkler.org> On Behalf 
Of Mike Hairfield via Sprinklerforum
Sent: Wednesday, January 26, 2022 8:08 AM
To: sprinklerforum@lists.firesprinkler.org
Cc: Mike Hairfield <fsl...@msn.com>
Subject: Re: question about Storage height

It should be 10 feet even though the other container is empty it's still 
plastic.

Mike
________________________________
From: Sprinklerforum <sprinklerforum-boun...@lists.firesprinkler.org> on behalf 
of Steve Mackinnon via Sprinklerforum <sprinklerforum@lists.firesprinkler.org>
Sent: Wednesday, January 26, 2022 9:02 AM
To: sprinklerforum@lists.firesprinkler.org
<sprinklerforum@lists.firesprinkler.org>
Cc: Steve Mackinnon <ste...@hartcorn.com>; Peter Howard <phow...@hartcorn.com>
Subject: question about Storage height

Good morning all,

We have a storage situation where the liquid commodity is in a 5 foot plastic 
storage cube, with an equally sized empty plastic container below.

The empty container below is only there to act as a spill collection vessel.

The question our office has been banging around, what is the storage height???

Would this be considered 5 feet of storage or 10 feet?

Would you take any exception to the plastic containers (like when we change the 
commodity classification with wood to plastic pallets)?

Thank you in advance
Steven
_______________________________________________
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
https://urldefense.com/v3/__https://na01.safelinks.protection.outlook.com/?url=http*3A*2F*2Flists.firesp__;JSUl!!B5cixuoO7ltTeg!QrCp0eJxS7Ot1mmwCscvaG11e7ELPRSGIBZ4XbEWUGOe2OHepszwwba4Vr7yVuqKYw$
rinkler.org%2Flistinfo.cgi%2Fsprinklerforum-firesprinkler.org&amp;data=04%7C
01%7C%7C0d961840310a423de85308d9e0d49405%7C84df9e7fe9f640afb435aaaaaaaaaaaa%
7C1%7C0%7C637788025897874973%7CUnknown%7CTWFpbGZsb3d8eyJWIjoiMC4wLjAwMDAiLCJ
QIjoiV2luMzIiLCJBTiI6Ik1haWwiLCJXVCI6Mn0%3D%7C3000&amp;sdata=gZPzEokK%2FC%2F
BPf%2FyCzVVjYGR3%2FRAFZEAkLsE2Cn2Qjk%3D&amp;reserved=0
_______________________________________________
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
https://urldefense.com/v3/__http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org__;!!B5cixuoO7ltTeg!QrCp0eJxS7Ot1mmwCscvaG11e7ELPRSGIBZ4XbEWUGOe2OHepszwwba4Vr5wa9shEw$
_______________________________________________
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
https://urldefense.com/v3/__http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org__;!!B5cixuoO7ltTeg!QrCp0eJxS7Ot1mmwCscvaG11e7ELPRSGIBZ4XbEWUGOe2OHepszwwba4Vr5wa9shEw$

_______________________________________________
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
https://urldefense.com/v3/__http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org__;!!B5cixuoO7ltTeg!QrCp0eJxS7Ot1mmwCscvaG11e7ELPRSGIBZ4XbEWUGOe2OHepszwwba4Vr5wa9shEw$
_______________________________________________
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
https://urldefense.com/v3/__http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org__;!!B5cixuoO7ltTeg!QrCp0eJxS7Ot1mmwCscvaG11e7ELPRSGIBZ4XbEWUGOe2OHepszwwba4Vr5wa9shEw$

________________________________

NOTICE - This communication may contain confidential and privileged information 
that is for the sole use of the intended recipient. Any viewing, copying or 
distribution of, or reliance on this message by unintended recipients is 
strictly prohibited. If you have received this message in error, please notify 
us immediately by replying to the message and deleting it from your computer.

________________________________

NOTICE - This communication may contain confidential and privileged information 
that is for the sole use of the intended recipient. Any viewing, copying or 
distribution of, or reliance on this message by unintended recipients is 
strictly prohibited. If you have received this message in error, please notify 
us immediately by replying to the message and deleting it from your computer.
_______________________________________________
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to