Putting out some feelers on this one.  NFPA 318 requires a .2/3000 in 
fabrication areas in semi-conductor manufacturing facilities.  We're trying to 
quantify the system area limitation and not everyone is on the same page.  NFPA 
13 is cited for design criteria beyond what is in 318, but the system 
protection area limits are based on occupancy groups or high piled storage.  
Obviously the density corresponds to OH II (52k) but the area of application 
doesn't.  We're still way below an extra hazard level of protection looking at 
the curve, but falling in the no mans land in between in total water demand I'm 
not sure if it's still reasonable to use 52k square feet as our benchmark.  It 
doesn't seem totally unreasonable since we could run into the same density/area 
combo in a OH II facility with combustible concealed spaces etc.  Anyone have 
thoughts or better yet direct experience with this?  The applicable standards 
are NFPA 318 - 2018, NFPA 13 - 2019 and IFC - 2019.

Mike Morey
CFPS 3229 * NICET S.E.T. 123677
Project Manager * Fire Protection Group
Shambaugh & Son, LP an EMCOR Company
7614 Opportunity Drive * Fort Wayne, IN * 46825
direct 260.487.7824 /  cell 260.417.0625 /  fax 260.487.7991
email mmo...@shambaugh.com



This message is for the named person's use only.  It may contain confidential, 
proprietary or legally privileged information. No confidentiality or privilege 
is waived or lost by any mistransmission.  If you receive this message in 
error, please  immediately delete it and all copies of it from your system, 
destroy any hard copies of it and notify the sender.  You must not, directly or 
indirectly, use, disclose, distribute, print, or copy any part of this message 
if you are not the intended recipient.

_________________________________________________________
SprinklerForum mailing list
Sprinklerforum@lists.firesprinkler.org
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org

Reply via email to