The role velocity plays is that friction loss is proportional to the square of 
the velocity. Using Darcy-Weisbach this holds “truer” at any velocity than 
Hazen-Williams does outside a certain range of velocities.
It’s interesting to calc using D-W with the weight density and viscosity of 
clean water at 40F and find the velocity producing the same friction loss as 
H-W for a particular pipe size and C-Factor. You should only try this at home 
nights and weekends though, as it can get pretty wild.
I’ve heard that when the founders were coming up with the pipe schedules, they 
assumed a minimum end head pressure and spacing (to determine the flow), added 
the flows along the way, and increased the pipe size when the velocity got to 
around 32 ft/s.

b

From: Bob Caputo <bcap...@firesprinkler.org>
Sent: Tuesday, March 15, 2022 11:16 AM
To: Byron Weisz <by...@cen-calfire.com>; Michael de Gabriele 
<mpdegabri...@gmail.com>; Sprinkler Academy - C Bilbo <prodesigngr...@msn.com>
Cc: travis.m...@mfpdesign.com; sprinklerforum@lists.firesprinkler.org
Subject: [Sprinklerforum] Re: [EXTERNAL] Re: Velocity - Rant

Two separate issues:

There is no safety margin required by NFPA standards with regard to the water 
supply test versus the system demand.  The annex recommends one but the AHJ has 
the purview to require one.  I have tried many times, to define a 10% or 5% 
required safety margin by submitting proposals to the NFPA 13 committee and 
none have passed.  Ken Isman from University of Maryland (formerly from NFSA) 
also pushed this issue passionately but failed to convince the committee that a 
safety margin is required, or that one can e defined for every project.  If 
your project is in the already populated area, you may not need one but if it’s 
a location where communities are being developed or factories and warehouses 
are being planned, 10% might not be enough.

The evaluation of water supplies is engineering as opposed to design.  A 
registered professional engineer should evaluate all of the issues surrounding 
a project to determine the adequacy of a water supply.  NFPA standards provide 
wide leeway for the AHJ to make decisions, since they are the ones who need to 
show up and fight a fire or access a building. It is within the purview of the 
AHJ to add a safety margin to a water supply where they determine one is needed.


The velocity issue is simple.  NFPA standards do not require or limit 
velocities anywhere except for the suction side of a fire pump.  NFPA 13 and 24 
did limit velocities many years ago but the reasons have long since been 
dispelled.  People though at faster velocities, the Hazen Williams formula was 
less accurate.  Joe Hankins once told me that FM’s velocity limits were created 
because they didn’t want 1” grids or systems that couldn’t be upgraded as 
tenants or owners changed hands or building uses.

The benefit of being old is knowing old stuff, as long as you can still 
remember it



[https://www.dropbox.com/s/g4h8r7hdtsr6154/AFSA_L.png?raw=1]
Bob Caputo, CFPS
President
American Fire Sprinkler Association
c:     760-908-7753
p:
214-349-5965 ext124
w:
firesprinkler.org<http://firesprinkler.org/>
[http://cdn2.hubspot.net/hubfs/184235/dev_images/signature_app/facebook_sig.png]<https://www.facebook.com/firesprinkler.org/>
  
[http://cdn2.hubspot.net/hubfs/184235/dev_images/signature_app/twitter_sig.png] 
<https://twitter.com/afsa/status/1039528345367732224>   
[http://cdn2.hubspot.net/hubfs/184235/dev_images/signature_app/linkedin_sig.png]
 <https://www.linkedin.com/company/american-fire-sprinkler-association-afsa-/>  
 
[http://cdn2.hubspot.net/hubfs/184235/dev_images/signature_app/instagram_sig.png]
 <https://www.instagram.com/firesprinklerorg/>

Expand your business with ITM.
Professionalize the role of your inspection team with AFSA’s comprehensive 
20-month ITM Inspector Development program<https://www.firesprinkler.org/itm> 
that provides a blended learning environment teamed with robust curriculum 
created by top industry leaders. Now enrolling for Spring 2022!

From: Byron Weisz <by...@cen-calfire.com<mailto:by...@cen-calfire.com>>
Sent: Tuesday, March 15, 2022 9:18 AM
To: Michael de Gabriele 
<mpdegabri...@gmail.com<mailto:mpdegabri...@gmail.com>>; Sprinkler Academy - C 
Bilbo <prodesigngr...@msn.com<mailto:prodesigngr...@msn.com>>
Cc: travis.m...@mfpdesign.com<mailto:travis.m...@mfpdesign.com>; 
sprinklerforum@lists.firesprinkler.org<mailto:sprinklerforum@lists.firesprinkler.org>
Subject: [Sprinklerforum] Re: [EXTERNAL] Re: Velocity - Rant

I think there are some good practices that need to be followed in the design of 
fire sprinkler systems and sometimes “simpler” is better. Treating the flow of 
water in fire sprinkler piping to other mechanical systems are not comparable. 
The obvious is a fire sprinkler system is designed for emergency use and other 
mechanical systems are in continuous use. Sadly, most Mechanical Engineers who 
write specifications for fire sprinkler design don’t understand the difference. 
I was taught that velocity in fire sprinkler piping was irrelevant and to my 
knowledge there is nothing stated in NFPA 13.

To continue the conversation there is no reference of a “safety margin” in NFPA 
13 either. I was told many years ago by this guy named Bob Caputo that NFPA 13 
allow you to design right to the design curve. Most jurisdictions in the 
Republic of California give water flow data from either the Fire Department or 
a Water Service Company to use for design of a system. This information is 
usually doctored in some way. So why would a designer take “doctored” water 
flow data and then include a 10% safety margin? Other than to meet a local 
requirement there is no reason. What makes no sense at all is to take 
“doctored” water flow information and use that information to size a fire pump 
to design an ESFR fire sprinkler system.

Again, the best person to answer the questions of velocity and safety margin in 
the design of a fire sprinkler system gracefully would be Bob.


Byron Weisz

Cen-Cal Fire Systems, Inc.
P.O. Box 1284
Lodi,  CA   95241
Phone (209) 334-9119
Fax      (209) 334-2923
Cell      (209) 993-8832
by...@cen-calfire.com<mailto:by...@cen-calfire.com>

This and any attached documents are for the use of the intended recipient(s) 
only and may contain information that is privileged, confidential, or work 
product that may be exempt from disclosure under applicable law. If you are not 
the intended recipient, any use, dissemination, distribution, or copying of 
this communication and any attachments is strictly prohibited, and you are 
hereby requested to delete this message and any attached documents, to destroy 
any printed copies, and to telephone or otherwise contact the sender 
immediately about the error.

From: Michael de Gabriele 
<mpdegabri...@gmail.com<mailto:mpdegabri...@gmail.com>>
Sent: Tuesday, March 15, 2022 5:46 AM
To: Sprinkler Academy - C Bilbo 
<prodesigngr...@msn.com<mailto:prodesigngr...@msn.com>>
Cc: travis.m...@mfpdesign.com<mailto:travis.m...@mfpdesign.com>; 
sprinklerforum@lists.firesprinkler.org<mailto:sprinklerforum@lists.firesprinkler.org>
Subject: [Sprinklerforum] Re: [EXTERNAL] Re: Velocity - Rant

You don't often get email from 
mpdegabri...@gmail.com<mailto:mpdegabri...@gmail.com>. Learn why this is 
important<http://aka.ms/LearnAboutSenderIdentification>
Hello All,
I hope that this email finds you well.
I practice fire protection in Australia, and recently the Australian standards 
have removed the requirements for maximum pipe work velocity in sprinkler 
systems.
We also design systems to NFPA and FM Global requirements when insurers request 
upgrades, and as of late, the insurer on one particular project queried the 
pipe work velocities. I couldnt find any reference to velocity limitations in 
NFPA 13.
I still try and keep my sprinkler pipe velocities down to a reasonable & 
practical value (6m/sec through valves and max. 10m/sec in pipe work as per the 
older/superseded code).

I am curious though to whether the Hzen Williams Formula produces greater 
errors as the Velocities Increase in the pipe? Has anyone ever seen a 
limitation to the Formula or come across any articles to this effect?

Looking forward to your response / comments / advice

Kind Regards
Michael de Gabriele
Fire Protections Engineer
mpdegabri...@gmail.com<mailto:mpdegabri...@gmail.com>

On Tue, Mar 15, 2022 at 10:48 PM Sprinkler Academy - C Bilbo 
<prodesigngr...@msn.com<mailto:prodesigngr...@msn.com>> wrote:
Hi Travis,

I learned many years ago the reason velocity restrictions have persisted.  In 
systems that have running water, the higher velocities wear the inner walls of 
the pipe/tube down over time.  The limits were intended to bolster system 
lifetime.
Mechanical engineers are the largest group responsible for specifying sprinkler 
systems and used the limits that seemed reasonable to them.
Of course, our systems are not flowing or circulating and these rules should 
not apply to dedicated fire protection piping.  We have only recently come away 
from having "closed loop circulating systems" being defined in the NFPA 13 
Standard.  And this is one of the reasons we used to do that.
About the only requirement I have seen in Fire Protection was the old rules 
from FM Global (last 10-15 years) where the underground systems had limits.  I 
believe those have been gone for a while.
However, some MILSPEC and certain States still have some requirements embedded 
in older sections of regulations.
Hope this helps.


It should be recognized that the above is my opinion as a member of the NFPA, 
and has not been processed as a formal interpretation in accordance with the 
NFPA Regulations Governing Committee Projects and should therefore not be 
considered, nor relied upon, as the official position of the the NFPA, nor any 
of their technical committees.

Sincerely,


Cecil Bilbo
Academy of Fire Sprinkler Technology
Decatur, IL
217.607.0325
www.sprinkleracademy.com<http://www.sprinkleracademy.com>
ce...@sprinkleracademy.com<mailto:ce...@sprinkleracademy.com>
??
OUR STUDENTS SAVE LIVES!!
________________________________
From: travis.m...@mfpdesign.com<mailto:travis.m...@mfpdesign.com> 
<travis.m...@mfpdesign.com<mailto:travis.m...@mfpdesign.com>>
Sent: Monday, March 14, 2022 5:41 PM
Cc: 
sprinklerforum@lists.firesprinkler.org<mailto:sprinklerforum@lists.firesprinkler.org>
 
<sprinklerforum@lists.firesprinkler.org<mailto:sprinklerforum@lists.firesprinkler.org>>
Subject: [Sprinklerforum] Re: [EXTERNAL] Re: Velocity - Rant


This was the “why” that I got:



We require a 10 psi margin for safety and to account for future degradation of 
water supply.  The 14 fps insures that the piping will be larger and is an 
added layer of margin for future development.



It wasn’t a fight the contractor wanted to go with since it was something he 
missed in the specs.  They had no explanation as to why 14 fps.



Please rate our customer 
service<https://survey.medallia.com/?emailsignature&fc=3539&bg=Fire%20and%20Fabrication>



Travis Mack, CFPS, CWBSP, RME-G, COC, SET

Senior Engineering Manager

MFP Design

480-505-9271 ext. 700 C: 480-272-2471

travis.m...@mfpdesign.com<mailto:travis.m...@mfpdesign.com>

www.mfpdesign.com<http://www.mfpdesign.com>



Send large files to us via: 
https://www.hightail.com/u/MFPDesign<https://na01.safelinks.protection.outlook.com/?url=https%3A%2F%2Fwww.hightail.com%2Fu%2FMFPDesign&data=02%7C01%7C%7C1121d49f9e6b4cf248f108d4df580e77%7C14e5497c16da42e69ffa77d19bafe511%7C0%7C0%7C636379016677342180&sdata=eGdMZGu2wXhUupGwgGTrqF3b54OP5%2BAZvlHhABSexWY%3D&reserved=0>



From: Ken Wagoner 
<k...@parsleyconsulting.com<mailto:k...@parsleyconsulting.com>>
Sent: Monday, March 14, 2022 3:36 PM
To: Travis Mack <travis.m...@mfpdesign.com<mailto:travis.m...@mfpdesign.com>>
Cc: 
sprinklerforum@lists.firesprinkler.org<mailto:sprinklerforum@lists.firesprinkler.org>
Subject: Re: [Sprinklerforum] Re: [EXTERNAL] Re: Velocity - Rant



Travis,

I've run up against that a time or two myself.  It honestly baffles me how 
those who have so limited an understanding of fire sprinkler systems mandate 
what we do.

I've usually responded in one of several ways.

1st, I ask them to show me where in any applicable code or standard they've 
found a limitation on velocities in above ground piping.  And, clearly, as you 
and others have said - they can't because it isn't there.  As far as NFPA is 
concerned it never was. A contact I had at NFPA a few years back told me of an 
"engineer" who called him and wanted to know when that had been removed from 
-13.  He did some research and found that it was never removed, because it was 
never there in the first place. That didn't go over well with the caller who 
was sure my contact was misleading him.

2nd, I acknowledge that the limitations on velocities in underground pipes on 
public property are established as another poster observe to lessen the 
deterioration caused from perpetually flowing water.  When I mention that pipe 
sizing on public property is their purview, and what is installed on private 
property they have no control over.  Usually my trump card in that argument is 
to ask why backflow preventers are usually at or near the property line.

3rd, and this works almost every time, I ask them to explain "why".  I don't 
hear many responses to that which make any sense as far as fire sprinklers go.

my thoughts only,

Ken Wagoner, SET
Parsley Consulting
500 West Mechanic Street
Harrisonville, Missouri 64701-2235
Phone: (760) 745-6181
Visit the 
website<https://linkprotect.cudasvc.com/url?a=http%3a%2f%2fwww.parsleyconsulting.com%2f&c=E,1,Y5zKJKPEh1mBEBqSR-VE9cUKl5y-eyP8BpvmE_5j9ZqW2eJbNphYzrCMBZ-2YuX6d-RRkHI4gQ1FV-cvOeCfRC58uZS9NiToZv2mx7909oCqLvCW_n5hDHeK&typo=1>

On 3/14/2022 3:33 PM, 
travis.m...@mfpdesign.com<mailto:travis.m...@mfpdesign.com> wrote:

I totally realize where all this comes from.  It just amazes me at times, how 
long incorrect information and lack of understanding of things can remain in an 
industry.  I always challenge anyone to show me in a copy of NFPA 13 anytime 
where it had velocity limits.  I’ve checked back as far as the 30’s and could 
never find it.



People always say, I know it was in there at one time.



Please rate our customer 
service<https://survey.medallia.com/?emailsignature&fc=3539&bg=Fire%20and%20Fabrication>



Travis Mack, CFPS, CWBSP, RME-G, COC, SET

Senior Engineering Manager

MFP Design

480-505-9271 ext. 700 C: 480-272-2471

travis.m...@mfpdesign.com<mailto:travis.m...@mfpdesign.com>

www.mfpdesign.com<http://www.mfpdesign.com>



Send large files to us via: 
https://www.hightail.com/u/MFPDesign<https://na01.safelinks.protection.outlook.com/?url=https%3A%2F%2Fwww.hightail.com%2Fu%2FMFPDesign&data=02%7C01%7C%7C1121d49f9e6b4cf248f108d4df580e77%7C14e5497c16da42e69ffa77d19bafe511%7C0%7C0%7C636379016677342180&sdata=eGdMZGu2wXhUupGwgGTrqF3b54OP5%2BAZvlHhABSexWY%3D&reserved=0>



From: Prahl, Craig/GVL <craig.pr...@jacobs.com><mailto:craig.pr...@jacobs.com>
Sent: Monday, March 14, 2022 1:30 PM
To: Brett Peters <br...@proudline.ca><mailto:br...@proudline.ca>; Travis Mack 
<travis.m...@mfpdesign.com><mailto:travis.m...@mfpdesign.com>
Cc: 
sprinklerforum@lists.firesprinkler.org<mailto:sprinklerforum@lists.firesprinkler.org>
Subject: RE: [EXTERNAL] [Sprinklerforum] Re: Velocity - Rant



What Brett said.



I have had more “discussions” on velocity and pressure loss where the 
challenger was quoting limits that are placed on totally unrelated type 
systems. Try to explain to them that those rules do not apply to fire 
protection systems and they’ll look at you like you’ve got a horn coming out of 
your forehead.  I’ve also had these types of artificial limitations placed by 
owners who have some “FP” person on staff who has never performed a flow test 
or developed a hydraulic calculation but did stay at a Holiday Inn Express 
which had sprinklers.



Craig Prahl | Jacobs | Group Lead/SME – Fire Protection | 
craig.pr...@jacobs.com<mailto:craig.pr...@jacobs.com> | 
www.jacobs.com<http://www.jacobs.com/>

1041 East Butler Road   Greenville, South Carolina  29606

CONTACT BY: email or MS TEAMS







From: Brett Peters <br...@proudline.ca<mailto:br...@proudline.ca>>
Sent: Monday, March 14, 2022 4:13 PM
To: travis.m...@mfpdesign.com<mailto:travis.m...@mfpdesign.com>
Cc: 
sprinklerforum@lists.firesprinkler.org<mailto:sprinklerforum@lists.firesprinkler.org>
Subject: [EXTERNAL] [Sprinklerforum] Re: Velocity - Rant



It's because they have velocity limits when sizing heating and water lines and 
can't wrap their heads around sprinkler hydraulics.

when you have constant water flow through piping, high velocity wears the pipe 
out faster, somehow they translate that to sprinkler pipe failure even though 
sprinkler pipe rarely even sees any water flow!



Thanks



Brett Peters

General Manager Installation & Design

Proudline Fire Protection Services Ltd.

br...@proudline.ca<mailto:br...@proudline.ca>

780 490 7602 office ext 202

780 490 7605 fax

780 777 0568 cell

780 718 2676 24h

Visit us at 
www.proudline.ca<https://urldefense.com/v3/__http:/www.proudline.ca/__;!!B5cixuoO7ltTeg!XuefiEhzuSpMkE5hwQfrMaq2esN89q-FRGseCr912x9x3M0x79mcWA0V05NMb4e_4w$>



[https://drive.google.com/uc?id=1OmoSKJ_6j8bUkKaO7Bn03FqLsLL_CGFg&export=download]
 
[https://drive.google.com/uc?id=12vmay3NIMK7kvNSKzKSwQ3QMUu4c0Pjh&export=download]
  
[https://drive.google.com/uc?id=1WooQGP1U-Z-tivGaOd9iUIJe1t5nDIjs&export=download]
  
[https://drive.google.com/uc?id=1MBUQypGGoakyf2Oz-f89so4CO5gWL-XH&export=download]
  
[https://drive.google.com/uc?id=1-auFTtN-brybbHNv2RnkM0NRf831e6rW&export=download]
  
[https://drive.google.com/uc?id=14_f6c1uVNDgMx_0OrApPsa-zCV1WCOMO&export=download]
  
[https://drive.google.com/uc?id=1kQhWctmizXAVYEesipCzOmZj6rp3W5J7&export=download]
  
[https://drive.google.com/uc?id=1cLsq8r4z61yUMJBu7OB2THA3zKwD16X4&export=download]





On Mon, Mar 14, 2022 at 1:50 PM 
<travis.m...@mfpdesign.com<mailto:travis.m...@mfpdesign.com>> wrote:

Does anyone have any idea where these engineers come up with the velocity 
limits?  We have one that they are requiring a 10 PSI margin (not an issue 
since AHJ requires 20%), but also limiting velocity to FOURTEEN fps.  There has 
never been a limit in NFPA 13.  The velocity that we determine is only based on 
a demand calc.  The water supply doesn’t know to reduce flow so that a 10 psi 
margin is maintained.  If a single sprinkler activates, that 1” arm over is 
going to see far greater than 14 fps.



It really just baffles me how this criteria has become so ingrained in the 
engineering culture.



Please rate our customer 
service<https://urldefense.com/v3/__https:/survey.medallia.com/?emailsignature&fc=3539&bg=Fire*20and*20Fabrication__;JSU!!B5cixuoO7ltTeg!XuefiEhzuSpMkE5hwQfrMaq2esN89q-FRGseCr912x9x3M0x79mcWA0V05PqkrhoUQ$>



Travis Mack, CFPS, CWBSP, RME-G, COC, SET

Senior Engineering Manager

MFP Design

480-505-9271 ext. 700 C: 480-272-2471

travis.m...@mfpdesign.com<mailto:travis.m...@mfpdesign.com>

www.mfpdesign.com<https://urldefense.com/v3/__http:/www.mfpdesign.com__;!!B5cixuoO7ltTeg!XuefiEhzuSpMkE5hwQfrMaq2esN89q-FRGseCr912x9x3M0x79mcWA0V05Muei1aEQ$>



Send large files to us via: 
https://www.hightail.com/u/MFPDesign<https://urldefense.com/v3/__https:/na01.safelinks.protection.outlook.com/?url=https*3A*2F*2Fwww.hightail.com*2Fu*2FMFPDesign&data=02*7C01*7C*7C1121d49f9e6b4cf248f108d4df580e77*7C14e5497c16da42e69ffa77d19bafe511*7C0*7C0*7C636379016677342180&sdata=eGdMZGu2wXhUupGwgGTrqF3b54OP5*2BAZvlHhABSexWY*3D&reserved=0__;JSUlJSUlJSUlJSUlJSU!!B5cixuoO7ltTeg!XuefiEhzuSpMkE5hwQfrMaq2esN89q-FRGseCr912x9x3M0x79mcWA0V05Mmw_OSKQ$>



SprinklerForum mailing list
Sprinklerforum@lists.firesprinkler.org<mailto:Sprinklerforum@lists.firesprinkler.org>
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org<https://urldefense.com/v3/__https:/lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org__;!!B5cixuoO7ltTeg!XuefiEhzuSpMkE5hwQfrMaq2esN89q-FRGseCr912x9x3M0x79mcWA0V05Pso7LieA$>



________________________________

NOTICE - This communication may contain confidential and privileged information 
that is for the sole use of the intended recipient. Any viewing, copying or 
distribution of, or reliance on this message by unintended recipients is 
strictly prohibited. If you have received this message in error, please notify 
us immediately by replying to the message and deleting it from your computer.





_________________________________________________________

SprinklerForum mailing list

Sprinklerforum@lists.firesprinkler.org<mailto:Sprinklerforum@lists.firesprinkler.org>

https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org





[https://ipmcdn.avast.com/images/icons/icon-envelope-tick-green-avg-v1.png]<http://www.avg.com/email-signature?utm_medium=email&utm_source=link&utm_campaign=sig-email&utm_content=emailclient>

Virus-free. 
www.avg.com<http://www.avg.com/email-signature?utm_medium=email&utm_source=link&utm_campaign=sig-email&utm_content=emailclient>



_________________________________________________________
SprinklerForum mailing list
Sprinklerforum@lists.firesprinkler.org<mailto:Sprinklerforum@lists.firesprinkler.org>