Good day all, it's been a while.  I'm still here for you old timers.

It appears the traditional 25% drop in residual pressure for satisfactory 
results has been modified to 10%, '22 edition 4.4.6.  I've looked in the 
committee reports and can't find why.  When I look in the enhanced content on 
Link it talks about 25% still.  So now I'm wondering if it's a typo. Anyone 
have an idea why this changed?

The option to flow system demand appears modified as well in 4.4.7 When 
conducting a flow test for the purpose of fire protection system design, the 
flow and pressure results should be adequate for the total demand of the 
system.  Like that's practical for high demand systems, lol.

Putting it together does it all mean for fire flow drop 10% and for system 
design we now HAVE to go to system demand?