From NFPA13, 2019 edition, table 20.14.2.2.3, it looks like maximum storage 
height is 35-feet in a 40-foot high building. 

If I am correct reading this, then they will have to Install a ceiling and you 
will have to redesign the system. 

Another alternative is to lower the storage to 6-feet which is probably not 
feasible. 

Just my opinion. 
Call Kemal in the Dallas office. 
Rick Matsuda 

> On Oct 26, 2022, at 11:14 AM, Jennifer Cornett <[email protected]> wrote:
> 
> I have a customer that has moved into a building with existing preaction 
> systems. They demoed out the protecto wire and racks so that it is wide open 
> and only roof system. 
> They now store idle wooden pallets in there up to 38' on the ground and the 
> building is 60' high at the peak. They don't have adequate heat, so wet is 
> out of question. Overhead system was calculated at .3/2600. What are my best 
> options to bring this up to code? Thank you.
> 
> Sincerely,
> 
> Jennifer Cornett, NICET SET
> Sprinkler Sales
> Firetrol Protection Systems, Inc.
> 1001 Ave. B
> Lubbock, Texas 79401
> Ph. 806-771-3500
> Cell 806-589-9630
> Fax 806-771-3501
> www.firetrol.net
> 
> Please Let Us Know How We Are Doing
> Click Here
> 
> 
> ____________________________________________________________
> This email is intended for the use of the individual or entity to which it is 
> addressed and may contain information that is privileged, confidential and 
> exempt from disclosure under applicable law.  If the reader of this email 
> message is not the intended recipient, or the employee or agent responsible 
> for delivery of the message to the intended recipient, you are hereby 
> notified that any dissemination, distribution or copying of this 
> communication is prohibited.  If you have received this email in error, 
> please notify us immediately by telephone at 806-771-3500 and also indicate 
> the sender's name.  Thank you.
> 
> 
> 
> 
> _________________________________________________________
> SprinklerForum mailing list:
> https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
> To unsubscribe send an email to [email protected]

_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
To unsubscribe send an email to [email protected]

Reply via email to