When I have come across it – it usually means what ever sort of standpipe connection the FD is ok with. We have done 1 outlet and 2 outlet types.
Matt From: Fpdcdesign <[email protected]> Sent: Wednesday, November 30, 2022 7:00 AM To: Discussion list on issues relating to automatic fire sprinklers <[email protected]> Subject: [Sprinklerforum] Roof Hydrant I am working on an existing 4 story building which is being retrofitted with a Class III standpipe system. We have been told that a ”roof hydrant” is required. I have not seen anything in 14 (2013 is what this jurisdiction is using) that specifically mentions a roof hydrant. Section 7.3.2 talks about a hose valve on the roof, which I assume is a single valve. I couldn’t find anything that requires any more, although there are a lot of images that show 2 or 3 outlets. What am I missing? Todd G Williams, PE Fire Protection Design/Consulting Stonington, CT 860-535-2080<tel:860-535-2080> (ofc) 860-554-7054<tel:860-554-7054> (fax) 860-608-4559<tel:860-608-4559> (cell)