I'm not aware of one. But please allow me to officially chortle at the fact that this guy has got a unit heater hanging in his glass room and he's concerned about the looks of a pendent sprinkler.
-Kyle M From: Matt Grise <[email protected]> Sent: Wednesday, December 28, 2022 8:48 AM To: Discussion list on issues relating to automatic fire sprinklers <[email protected]> Subject: [EXTERNAL] [Sprinklerforum] high-temp concealers Is anyone aware of a high-temperature rated concealed sprinkler? We have a small vestibule with a large unit heater where the owner would like a concealed sprinkler, but I am not having any luck finding a concealer with a high-temperature rating. There is not any space in the room outside of the high-temp zone shown in figure 8.3.2.5 (NFPA 13, 2016) Also - it needs to be a pendant. All of the walls of the vestibule are glass. Thanks! Matt