You didn't specify which yr. of 13R. But in the 2016 it talks about areas
outside dwelling units in sections 6.2.2 and 7.2. 

 

6.2.2 gives a list of allowable areas.

 

7.2 give you the criteria for these areas.

 

My guess is this area is probably going to be used for storage so most
likely OH1. Per 13R (2016) your limited to 500sf or less of compartmented
areas with 30min fire rated construction. (7.2.4.1)

 

My opinion would be your probably going to have to use QR sprinklers.

 

Thanks,

 




 



 

 

Dane Long, AET
Engineering Technician | Bamford Fire Sprinkler Co., Inc.
P:    785.825.7710
F:    785.825.0667
A:   1383 W. North Street  Salina, KS  67401



 

 

From: Bobby Welch <bobby.we...@koorsen.com> 
Sent: Thursday, January 19, 2023 10:42 AM
To: Discussion list on issues relating to automatic fire sprinklers
<sprinklerforum@lists.firesprinkler.org>
Subject: [Sprinklerforum] 13R basements

 

When sprinkling a basement in a 13R system can residential heads be used,
when the compartments are 1000 sq. ft. and the structure is exposed (2"x12"
truss)?