If the zone control has a control valve, check valve, drain, flow, and gauge 
then yep. In this case though you generally wouldn’t have that single “system 
riser” before those 4 assemblies though. You’d either just have your backflow 
or fire pump setup feeding the 4 zones in a manifold arrangement.

From: Fpdcdesign <fpdcdes...@gmail.com>
Sent: Wednesday, February 15, 2023 11:10 AM
To: Discussion list on issues relating to automatic fire sprinklers 
<sprinklerforum@lists.firesprinkler.org>
Subject: [Sprinklerforum] Re: Zone valves and maximum area

If the floor control assembly is satisfactory for subdividing a system 
horizontally to meet the 52000 restriction, let me pose this:

Suppose you have a 160000 sqft warehouse. You have a single system riser that 
feeds four 40000 sqft grids, each with a floor control assembly. Good or no? 
Same principle.




On Feb 14, 2023 at 7:27 PM, <Dwight Havens<mailto:dhavensh...@yahoo.com>> wrote:

 Todd,

I agree with Brett, that you have two separate systems when you have a control 
valve and flow switch for each one, so you won't be exceeded system area 
limitations in NFPA 13.

As a firefighter, I'm more concerned that they need to have a common fire 
department connection (feeding both risers), so that the fire department can 
supplement the sprinkler and standpipe systems without attaching to an 
incorrect connection.

Dwight H. HavensFire Code Official-Retired.

    On Tuesday, February 14, 2023 at 06:18:39 PM EST, Brett Peters 
<br...@proudline.ca<mailto:br...@proudline.ca>> wrote:



 If it's one second floor zone than it's a problem, if it's a standpipe riser 
with 2 separate zone controls for each section of the 2nd floor then it's fine





Thanks

Brett Peters

General Manager Installation & DesignProudline Fire Protection Services 
Ltd.brett@proudline.ca780<mailto:Ltd.brett@proudline.ca780> 490 7602 office ext 
202780 490 7605 fax780 777 0568 cell780 718 2676 24hVisit us at 
www.proudline.ca<http://www.proudline.ca>

Proudline now offers ULc listed monitoring services, please contact 
m...@proudline.ca<mailto:m...@proudline.ca> for more information











On Tue, Feb 14, 2023 at 3:17 PM Fpdcdesign 
<fpdcdes...@gmail.com<mailto:fpdcdes...@gmail.com>> wrote:



I am working on an old 4 story mill structure with existing sprinkler systems. 
This is a property that has been renovated quite a bit since the mid 1800s when 
it was built. The section I am working on consists of a building about 70ft x 
500ft. There is a somewhat similar but equal sized building that goes at a 90 
degree angle. The combined structure is a giant L. My project is a renovation 
to the 2nd floor of the first building for apartments. The other building has 
been renovated into a school, a couple of commercial spaces and apartments.

The building I am working on has an 8” service coming in and the other building 
has a 10” service.

At some point, the sprinkler system in the space I am working in has been 
replaced, probably with the last 20 years. This sprinkler system is connected 
to a standpipe in the school building and has a zone valve and flow switch. 
This connects to the riser in the school building and not the one in the 
building where the project is.  If both 2nd floors are fed from the same riser, 
then the 2nd floor has 70000 sqft of system on one level fed from a single 
riser, but on 2 zones.

The first floor has a hodge podge of connections I have not explored as it is 
not part of my contract. I have no idea what is going on the 3rd of 4th for the 
same reason.

Am i reading it right that this is a problem?

Todd G Williams, PEFire Protection Design/ConsultingStonington, CT860-535-2080 
(ofc)860-554-7054  (fax)860-608-4559 (cell)

_________________________________________________________

SprinklerForum mailing list:

https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org

To unsubscribe send an email to 
sprinklerforum-le...@lists.firesprinkler.org<mailto:sprinklerforum-le...@lists.firesprinkler.org>



_________________________________________________________

SprinklerForum mailing list:

https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org

To unsubscribe send an email to 
sprinklerforum-le...@lists.firesprinkler.org<mailto:sprinklerforum-le...@lists.firesprinkler.org>



_________________________________________________________

SprinklerForum mailing list:

https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org

To unsubscribe send an email to 
sprinklerforum-le...@lists.firesprinkler.org<mailto:sprinklerforum-le...@lists.firesprinkler.org>
_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
To unsubscribe send an email to sprinklerforum-le...@lists.firesprinkler.org

Reply via email to