A.8.6.5.3.3 When obstructions are located more than 18in. below the sprinkler deflector, an adequate spray pattern develops and obstructions up to and including 4 ft. wide do not require additional protection underneath. Examples are ducts, decks, open grate flooring, catwalks, cutting tables, overhead doors, soffits, ceiling panels, and other similar obastrucitons.
-----Original Message----- From: Jason Moore <ja...@vvfire.com> Sent: Monday, March 6, 2023 3:32 PM To: Discussion list on issues relating to automatic fire sprinklers <sprinklerforum@lists.firesprinkler.org> Subject: [Sprinklerforum] Re: Ductwork more than 18 inches below a sprinkler line and less than 4'-0" in width I'd look at 8.6.5.2.1.3 -----Original Message----- From: Sean Lockyer <slock...@aitlifesafety.com> Sent: Monday, March 6, 2023 12:19 PM To: Discussion list on issues relating to automatic fire sprinklers <sprinklerforum@lists.firesprinkler.org> Subject: [Sprinklerforum] Re: Ductwork more than 18 inches below a sprinkler line and less than 4'-0" in width Craig - this is a standard sprinkler in question, so the first figure I went to is Figure 8.6.5.1.2 (a). Seeing as that this is not a light hazard area, Figure 8.6.5.2.2 would not apply. I then wanted to see if there was consensus that section 8.6.5.3.1 could be considered since the obstruction is more than 18" below the deflector, but after re-reading everything again, it would appear that the only "out" I have is to try to have the obstruction equally spaced between (2) lines as allowed for in 8.6.5.1.2 (2) since the ductwork does not exceed 4'-0". -----Original Message----- From: Prahl, Craig <craig.pr...@jacobs.com> Sent: Monday, March 6, 2023 12:24 PM To: Discussion list on issues relating to automatic fire sprinklers <sprinklerforum@lists.firesprinkler.org> Subject: [Sprinklerforum] Re: Ductwork more than 18 inches below a sprinkler line and less than 4'-0" in width Here's a question, what did you find out in NFPA 13 when looking at the specific obstruction rules for the type of sprinkler you are providing? Determining if you have an obstruction problem isn't limited to just the general >48" and 18" clearance rules. Craig Prahl | Jacobs | Group Lead/SME - Fire Protection | craig.pr...@jacobs.com | www.jacobs.com 1041 East Butler Road Greenville, South Carolina 29606 CONTACT BY: Phone 1-864-676-5252, Email or MS TEAMS -----Original Message----- From: Sean Lockyer <slock...@aitlifesafety.com> Sent: Monday, March 6, 2023 12:10 PM To: Discussion list on issues relating to automatic fire sprinklers <sprinklerforum@lists.firesprinkler.org> Subject: [EXTERNAL] [Sprinklerforum] Ductwork more than 18 inches below a sprinkler line and less than 4'-0" in width I have a situation in which there are two HVAC trunklines that are almost right next to two of my sprinkler lines. However, I am hanging these lines up in the bar joist space and the trunklines are a good 4'-0" below my lines (trunklines are hanging well below the trusses) and the trunklines are NOT 4'-0" in width (The max width is about 3'-2"). Since both HVAC lines are more than 18" below the deflector and since neither exceeds 4'-0" in width, would they still be considered obstructions ? Sean Lockyer Project Designer AITLifeSafety _________________________________________________________ SprinklerForum mailing list: https://urldefense.com/v3/__https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org__;!!B5cixuoO7ltTeg!ElbpJEicgs1bXe9Qi4kWgI0QoAheDj6xPkVW7iDng4K-b-WXxlyR7TNkUEX3dYtK68RtR3LdeE_OeCvqoavkYkSA$ To unsubscribe send an email to sprinklerforum-le...@lists.firesprinkler.org ________________________________ NOTICE - This communication may contain confidential and privileged information that is for the sole use of the intended recipient. Any viewing, copying or distribution of, or reliance on this message by unintended recipients is strictly prohibited. If you have received this message in error, please notify us immediately by replying to the message and deleting it from your computer. _________________________________________________________ SprinklerForum mailing list: https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org To unsubscribe send an email to sprinklerforum-le...@lists.firesprinkler.org _________________________________________________________ SprinklerForum mailing list: https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org To unsubscribe send an email to sprinklerforum-le...@lists.firesprinkler.org _________________________________________________________ SprinklerForum mailing list: https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org To unsubscribe send an email to sprinklerforum-le...@lists.firesprinkler.org _________________________________________________________ SprinklerForum mailing list: https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org To unsubscribe send an email to sprinklerforum-le...@lists.firesprinkler.org