Anthony,

 

I feel there might be a few sections you need to look at regarding this 
question. 

 

For me I would start at 8.6.5.2 Obstructions to Sprinkler Discharge Pattern 
Development.

 

8.6.5.2.1.1 Continuous or noncontinuous obstructions less than or equal to 18 
in. (457 mm)

below the sprinkler deflector that prevent the pattern from fully developing 
shall comply with

8.6.5.2.

 

The section above lays the ground work for the 18in requirement (8.6.5.2). Then 
I would look at 8.6.5.2.1.3* Minimum Distance from Obstructions.

 

8.6.5.2.1.4* For light and ordinary hazard occupancies, structural

members only shall be considered when applying the requirements

of 8.6.5.2.1.3.

 

IMHO Because it specifically says “structural members only shall be considered” 
I believe the intent of this section is to allow for us to not provide 
sprinklers on both side to a reasonable degree, meaning we’re able to get water 
on both sides of the obstruction as long as its not a structural member.

 

Thanks,

 




 



 

 

Dane Long, AET
Engineering Technician | Bamford Fire Sprinkler Co., Inc.
P:    785.825.7710
F:    785.825.0667
A:   1383 W. North Street  Salina, KS  67401



 

 

From: Anthony Johnson <mountainfirepr...@gmail.com> 
Sent: Thursday, March 9, 2023 2:26 PM
To: Discussion list on issues relating to automatic fire sprinklers 
<sprinklerforum@lists.firesprinkler.org>
Subject: [Sprinklerforum] Re: Duct obstruction criteria in LH attic

 

The 3x rule is the only one we think would apply but it only applies to 
structural components.

 

Best Regards,

Anthony Johnson

Mountain Fire Protection

'Saving Lives and Valuing Property'

 

On Thu, Mar 9, 2023 at 12:58 PM Taylor Schumacher <tay...@sfsprinkler.com 
<mailto:tay...@sfsprinkler.com> > wrote:

When you cannot apply one of the obstruction rules, it does not mean that there 
isn’t an obstruction. 

 

If you think about this scenario the same way you would with sprinklers 
directly attached to a pipe, that’s where to start. Look at the 3x rule or 
sprinklers on each side.

 

 

Taylor Schumacher

Security Fire Sprinkler <http://www.j-berd.com/>  

1 Industrial Blvd | Sauk Rapids, MN 56379

Office: 320.656.0847 | Direct: 320.640.7050

 

From: matthew.will...@ferguson.com <mailto:matthew.will...@ferguson.com>  
<matthew.will...@ferguson.com <mailto:matthew.will...@ferguson.com> > 
Sent: Thursday, March 09, 2023 12:37 PM
To: sprinklerforum@lists.firesprinkler.org 
<mailto:sprinklerforum@lists.firesprinkler.org> 
Subject: [Sprinklerforum] Re: Duct obstruction criteria in LH attic

 

I believe however, the intent of the section must still be applied. Water on 
both sides.

Not sure in the 13 edition the location, but in the 19 it is 10.2.7.1.2.

We are referred back to it as applicable from the 3 times section.

 

Sprinklers spaced on opposing sides, not to exceed the max half distance.

 

R/

Matt

 

Please rate our customer service 
<https://survey.medallia.com/?emailsignature&fc=3539&bg=Fire%20and%20Fabrication>
 

 

Matthew J. Willis, CWBSP, CET

Engineering Designer IV

FERGUSON FIRE DESIGN, LLC

A Wholly Owned Subsidiary of Ferguson Fire & Fabrication, LLC

401 N 5th Street

Suite 448

Wausau, WI 54403

C: 307-236-8249

matthew.will...@ferguson.com <mailto:matthew.will...@ferguson.com> 

www.FergusonFire.com <http://www.fergusonfire.com/> 

 

From: Anthony Johnson <mountainfirepr...@gmail.com 
<mailto:mountainfirepr...@gmail.com> > 
Sent: Thursday, March 9, 2023 11:24 AM
To: sprinklerforum@lists.firesprinkler.org 
<mailto:sprinklerforum@lists.firesprinkler.org> 
Subject: [Sprinklerforum] Duct obstruction criteria in LH attic

 

I have an elementary question but know there are varying opinions on the topic. 
The situation is a tight unused attic space in a LH occupancy. Our upright 
sprinkler deflector will be 3" above the ductwork. Evaluating all of the 
obstruction criteria presented in NFPA we've essentially came to the conclusion 
that the ductwork would not pose an obstruction but came to this conclusion 
mainly by process of elimination. The beam-rule would not apply since the 
ductwork is below the deflector. The 3X rule is only for structural components 
in light and ordinary hazards and the 'wide obstruction' rule would not apply 
since the ductwork is only 24" wide.  That only leaves the 'suspended or floor 
mounted vertical obstructions' rule of 8.6.5.2.2 ('2013 ed) but it specifically 
mentions free standing partitions, privacy curtains and "similar obstructions". 
I don't think duct-work is a similar obstruction. I would like to have my ducks 
in a row if this design approach should be questioned but also want to make 
sure I have a sound design. Is our reasoning correct that essentially if the 
sprinkler deflector is above the duct water will spray on both sides and the 
duct would not pose as an obstruction?

 

Best Regards,

Anthony Johnson

Mountain Fire Protection

'Saving Lives and Valuing Property'


_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
To unsubscribe send an email to sprinklerforum-le...@lists.firesprinkler.org 
<mailto:sprinklerforum-le...@lists.firesprinkler.org> 

_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
To unsubscribe send an email to sprinklerforum-le...@lists.firesprinkler.org

Reply via email to