Question concerning Fire Sprinklers in Racking:

Scenario.....

Got called out to a Home Improvement Store who had their Paint Racks moved and 
when they did they had the Piping in the Racks removed by a Company however 
this Company did not return to put the piping back in thus my company being 
called out to fix the issue.  When we started to evaluate the situation we were 
told that the Racking Size had not changed and the Hazard had not either 
however once we started the job and got to the point where the Piping that was 
removed be put back in we found that the Rack Size was different and the piping 
set up was not correct for the length.

Rack Length: 54' 9"
Total Pipe Network: 55' 10"
Sprinkler Heads 50" apart

The Piping Network was all Pre-Fab welded Pipe.


Question is with the change is setup does the Sprinkler System need to be 
looked at by an Engineer and have plans drawn up or can this all be done 
without going to that length?

Does it need to be Re-Calculated?
_________________________________________________________