Correction...not listed...new technology.

Ryan L. Hinson, PE*, SET**  \  Burns & McDonnell
Associate Fire Protection Engineer
O 612-900-3755 \  M 763-688-4045 \  F 952-229-2923
[email protected]<mailto:[email protected]>  \  
burnsmcd.com<http://www.burnsmcd.com/>
8201 Norman Center Drive, Suite 500  \  Minneapolis-St. Paul, MN 55437
*Registered in: AK, LA, MD, MN, PA, TX, & UT
**NICET IV - Water-Based Systems Layout

From: Hinson, Ryan <[email protected]>
Sent: Wednesday, July 19, 2023 4:20 PM
To: Discussion list on issues relating to automatic fire sprinklers 
<[email protected]>
Subject: [Sprinklerforum] Re: Hangers on Seismic swing joint

Metraflex has a listed seismic breakaway hanger for just such a use:
https://www.metraflex.com/seismic-applications/


Ryan L. Hinson, PE*, SET**  \  Burns & McDonnell
Associate Fire Protection Engineer
O 612-900-3755 \  M 763-688-4045 \  F 952-229-2923
[email protected]<mailto:[email protected]>  \  
burnsmcd.com<http://www.burnsmcd.com/>
8201 Norman Center Drive, Suite 500  \  Minneapolis-St. Paul, MN 55437
*Registered in: AK, LA, MD, MN, PA, TX, & UT
**NICET IV - Water-Based Systems Layout

From: James Crawford <[email protected]<mailto:[email protected]>>
Sent: Wednesday, July 19, 2023 4:13 PM
To: 
[email protected]<mailto:[email protected]>
Subject: [Sprinklerforum] Hangers on Seismic swing joint

NFPA #13 (2013) 9.3.3 Seismic Separation Assembly

There has been some discussion between the designers and the field staff on 
whether you can put a hanger on anything other then the pipes shown as "A" & 
"B" on Figure A.9.3.3(a)

Background 8" feed main crosses the seismic separation.

Field staff say that due to the weight of the pipe and the flexible fittings, a 
hanger is required to stop it from swinging down.

Office staff say no hanger as it would defeat the purpose of the swing joint as 
it would restrict movement.

Comments or background either way as we can find nothing in the code for either 
option.


Thank You

James Crawford
Phaser Fire Protection Ltd.
Phone 604-888-0318
Cel: 604-790-0938
Email [email protected]<mailto:[email protected]>
Web: www.phaserfire.ca<http://www.phaserfire.ca/>

_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
To unsubscribe send an email to [email protected]

Reply via email to