I don't know of a requirement for flanged fittings in the suction side. OS&Y 
valves typically came FxF and hence the suction side fittings would all be 
flanged. Grooved OS&Y is becoming more popular... That being said, I have yet 
to see a pump with grooved inlets and outlets.

Pros to all grooved are they are quicker to install.
Pros to all flanged is they create a more stable/sturdy connection.


Taylor Schumacher
Security Fire Sprinkler<http://www.j-berd.com/>
1 Industrial Blvd | Sauk Rapids, MN 56379
Office: 320.656.0847 | Direct: 320.640.7050

From: Brian Harris <[email protected]>
Sent: Tuesday, September 12, 2023 7:48 AM
To: [email protected]
Subject: [Sprinklerforum] Pump Suction Components


Caution: This email originated from outside your organization. Please take care 
when clicking links or opening attachments.


I've seen two schools of thought with regard to pump suction components. One 
way is flanged on the suction side and grooved on the discharge. The other is 
all grooved. I can; t see where NFPA-20 requires it either way. What's the 
popular choice and are there pro's & cons?