[image: image.png]
18 risers , 40,000 sqft      (cherry picked the dimensions)


On Tue, Dec 19, 2023 at 12:05 PM Prahl, Craig <craig.pr...@jacobs.com>
wrote:

> I need a sanity check.
>
>
>
> I have a micro-electronics clean room area.  H-5 occupancy. The
> interstitial space above is above 15 ft high and has catwalks which are
> above the cleanroom ceiling.  Architects have deemed the interstitial space
> as “Equipment Platforms”, unoccupied space.
>
>
>
> Referencing IBC/IFC 2021, NFPA 13, 2019
>
>
>
> Both the clean room and the interstitial space require full sprinkler
> protection per the building code, typically OH-2.
>
>
>
> Based on NFPA 13, the maximum area for the OH system is 52,000 sq. ft.
>
>
>
> Per 2019 NFPA 13, 4.5.2 if the area is considered a mezzanine there is no
> requirement to include the sq. footage of the interstitial space as part of
> the system area.  However, the interstitial space has a substantial ceiling
> assembly between it and the occupied clean room below so it’s closer in
> definition to an attic space or non-combustible concealed space with no
> provision for storage.  Access is restricted and limited.
>
>
>
> Overall the clean room is around 700,000 sq. ft. total so I’ve got a LOT
> of systems and am trying to determine size and quantity of riser rooms.
>
>
>
> *So, does it make sense to not include the area of the interstitial space
> in determining the number of risers.  Basically one OH system can cover
> 52,000 sf of clean room and 52,000 sq. ft. of interstitial space?  *
>
>
>
>
>
> Craig Prahl | Jacobs | Fire Protection SME – Special Hazards |
> craig.pr...@jacobs.com | www.jacobs.com
> <https://urldefense.com/v3/__http:/www.jacobs.com/__;!!KZTdOCjhgt4hgw!-_khxU8gU0_6jc895I7kRbnU8JghRDsWgqOblZ4jr7Qp2IVbR30VYw_hWvNFtphnl0uWpB9KIvbYi1pvZz4$>
>
> 1041 East Butler Road   Greenville, South Carolina  29606
>
> CONTACT BY: Phone 1-864-676-5252, Email or MS TEAMS
>
> ------------------------------
>
> NOTICE - This communication may contain confidential and privileged
> information that is for the sole use of the intended recipient. Any
> viewing, copying or distribution of, or reliance on this message by
> unintended recipients is strictly prohibited. If you have received this
> message in error, please notify us immediately by replying to the message
> and deleting it from your computer.
>
> _________________________________________________________
> SprinklerForum mailing list:
> https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
> To unsubscribe send an email to
> sprinklerforum-le...@lists.firesprinkler.org
>
_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
To unsubscribe send an email to sprinklerforum-le...@lists.firesprinkler.org

Reply via email to