NFPA 25 added a section regarding this in 2023.

8.3.3.11: Where simultaneous operation of multiple pumps is required to meet 
the water-based system demand for flow and pressure, the requirements of 
8.3.3.10(2) shall be repeated at each flow condition with all pumps operating 
simultaneously.

So, your test-header will need to accommodate the combined flow.

Hope this helps!
Eric Rieve, SET
Rieve Fire Protection

From: Fpdcdesign <fpdcdes...@gmail.com>
Sent: Monday, January 29, 2024 11:51 AM
To: Discussion list on issues relating to automatic fire sprinklers 
<sprinklerforum@lists.firesprinkler.org>
Subject: [Sprinklerforum] Re: Fire Pump testing procedures

I would think you would need to do both, at least initially. Individually to 
find out that each pump is working correctly itself and both to verify that the 
full demand can be met.

For a future testing program, probably something specialized would be needed. 
Make sure it is available in writing.




On Jan 29, 2024 at 11:45 AM, <Craig Prahl<mailto:craig.pr...@jacobs.com>> wrote:
I have a project that requires two 1500 gpm pumps to meet the most demanding 
system requirements.   Client doesn’t want any pumps over 1500 gpm.  Long story.

As far as testing, would you test each pump individually or together or  ??

Trying to establish what we need as far as a test header.

Thanks.

Craig Prahl | Jacobs | Fire Protection SME – Special Hazards | 
craig.pr...@jacobs.com<mailto:craig.pr...@jacobs.com> | 
www.jacobs.com<https://urldefense.com/v3/__http:/www.jacobs.com/__;!!KZTdOCjhgt4hgw!-_khxU8gU0_6jc895I7kRbnU8JghRDsWgqOblZ4jr7Qp2IVbR30VYw_hWvNFtphnl0uWpB9KIvbYi1pvZz4$>
1041 East Butler Road   Greenville, South Carolina  29606
CONTACT BY: Phone 1-864-676-5252, Email or MS TEAMS


________________________________

NOTICE - This communication may contain confidential and privileged information 
that is for the sole use of the intended recipient. Any viewing, copying or 
distribution of, or reliance on this message by unintended recipients is 
strictly prohibited. If you have received this message in error, please notify 
us immediately by replying to the message and deleting it from your computer.
_________________________________________________________ SprinklerForum 
mailing list: 
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org To 
unsubscribe send an email to 
sprinklerforum-le...@lists.firesprinkler.org<mailto:sprinklerforum-le...@lists.firesprinkler.org>
_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
To unsubscribe send an email to sprinklerforum-le...@lists.firesprinkler.org

Reply via email to