Why can’t you use a K16.8 CMSA instead of an ESFR? Controls mode design might 
be a little more friendly than extinguishing mode.   
  
  
  
  
  
  
  

  
  
>   
> On Feb 8, 2024 at 12:42 PM,  <Ken Wagoner 
> (mailto:k...@parsleyconsulting.com)>  wrote:
>   
>   
>   I'm a bit late to this discussion, however....
>   
>  When I look at the added flow requirements in §22.4.2.4 I note that this 
> application is only for "area/density" design criteria, and I am skeptical to 
> refer this to an ESFR system, which is certainly not "area/density."
>   
> Ken Wagoner, SET
>   Parsley Consulting
>  500 West Mechanic Street
>  Harrisonville, Missouri 64701-2235
>   Phone: (760) 745-6181
>    Visit the website 
> (https://linkprotect.cudasvc.com/url?a=http%3a%2f%2fwww.parsleyconsulting.com%2f&c=E,1,Y5zKJKPEh1mBEBqSR-VE9cUKl5y-eyP8BpvmE_5j9ZqW2eJbNphYzrCMBZ-2YuX6d-RRkHI4gQ1FV-cvOeCfRC58uZS9NiToZv2mx7909oCqLvCW_n5hDHeK&typo=1)
>    
>
>   
>
>   
>   
> On 2/8/2024 11:30 AM, Ben Young wrote:
>   
> >     
> > Sorry, i meant 23.4.4.2.4 not 23.4.4.2.3
> >   
> >   
> >   
> >
> >  Benjamin Young
> >       
> >
> >   
> >
> >   
> >   
> > On Thu, Feb 8, 2024 at 12:23 PM Ben Young  <derblitzkrie...@gmail.com 
> > (mailto:derblitzkrie...@gmail.com)>  wrote:
> >   
> > >   
> > > In the 2016 edition, check out sections 23.4.4.2.3 and 23.4.4.2.5
> > >   
> > >
> > >   
> > > Use those to add phantom flow based on the minimum flow from 12 
> > > sprinklers.
> > >   
> > >
> > >   
> > > It's a variation on the theme but it should satisfy the ahj.
> > >   
> > >   
> > >   
> > >
> > >  Benjamin Young
> > >       
> > >
> > >   
> > >
> > >   
> > >   
> > > On Thu, Feb 8, 2024 at 11:55 AM Matt Grise  <mattgri...@gmail.com 
> > > (mailto:mattgri...@gmail.com)>  wrote:
> > >   
> > > >   
> > > > We are looking at an auto repair facility that has a very small tire 
> > > > storage room (apx 300sf). The tire storage space is open on one side to 
> > > > the misc parts storage area (short-shelf OH2). Our thought was to 
> > > > protect the tire storage space with a small ESFR system that extends 
> > > > 15' into the misc parts storage area. The other 3 sides of the tire 
> > > > storage room are CMU and extend to the deck.  
> > > >
> > > >   
> > > > Even with   the 15' extension into the lesser hazard area, there are 
> > > > only 6 ESFR sprinklers needed. (2 heads on 3 lines) = 540sf.   
> > > >   
> > > >
> > > >   
> > > > Based on the annex commentary in NFPA 13 2016 A11.1.2, our plan was to 
> > > > calc the 6 esfr heads (the full higher-hazard area plus 15' = 540sf) 
> > > > along with 960sf    at .2gpm/sf to round out the larger of the two 
> > > > operating areas.
> > > >   
> > > >
> > > >   
> > > >
> > > >   
> > > > We received some pushback because there is no ESFR design criteria that 
> > > > only uses 6 heads, so the plan reviewer was concerned that we were not 
> > > > following the 12-head design for an ESFR system.
> > > >   
> > > >
> > > >   
> > > > There was a suggestion that we should pretend there were 12 heads and 
> > > > calc a 12 head area (even though 6 would never be installed).I figured 
> > > > that since we were calculating ALL of the ESFR heads in the building, 
> > > > that would be ok.
> > > >   
> > > >
> > > >   
> > > > Has anyone seen anything like this before? Any thoughts?
> > > >   
> > > >
> > > >   
> > > > Thanks!
> > > >   
> > > >
> > > >   
> > > > Matt Grise
> > > >   
> > > >
> > > >   
> > > >
> > > >     
> > > >  _________________________________________________________
> > > >  SprinklerForum mailing list:
> > > >   
> > > > https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
> > > >  To unsubscribe send an email to  
> > > > sprinklerforum-le...@lists.firesprinkler.org 
> > > > (mailto:sprinklerforum-le...@lists.firesprinkler.org)             
> >     
> >  _________________________________________________________ SprinklerForum 
> > mailing list:  
> > https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org 
> >  To unsubscribe send an email to  
> > sprinklerforum-le...@lists.firesprinkler.org 
> > (mailto:sprinklerforum-le...@lists.firesprinkler.org)   
>
>   
>  _________________________________________________________ SprinklerForum 
> mailing list: 
> https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org 
> To unsubscribe send an email to sprinklerforum-le...@lists.firesprinkler.org  
>           
_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
To unsubscribe send an email to sprinklerforum-le...@lists.firesprinkler.org

Reply via email to