Jackie,
As I read this section. it says that your deflector can be no more than
1" below the bottom of the concrete tee. If it is above the bottom of
the tee, than it must comply with the beam rule. If the sprinkler is
_<_ 12" away than it can be set at 0" above the tee, if it is 1' to <18"
than it can be no more than 2-1/2" above the tee, and etc....
/Thank you,
Bob Knight, CET III//
/*/Fire by Knight, LLC/*/
//208-318-3057/
FIREBYKNIGHT
On 2/9/2024 2:37 PM, Jackie Ward wrote:
I have 18” wide concrete beams extending 24” from the bottom of the
deck on 7’-0” centers.
NFPA-13 (2016) 8.6.4.1.2 Obstructed Construction (5)* Installed with
deflectors of sprinklers under concrete tee construction with stems
spaced less than 71⁄2 ft (2.3 m) on centers, regardless of the depth
of the tee, located at or above a horizontal plane 1 in. (25 mm) below
the bottom of the stems of the tees and complying with Table 8.6.5.1.2.
A.8.6.4.1.2(5) For concrete joists spaced less than 3 ft (900 mm) on
center, the rules for obstructed construction shown in 8.6.4.1.2
apply. For concrete tee construction with stems spaced less than 7 ft
6 in. (2.3 m) on center, the sprinkler deflector can be located at or
above a horizontal plane 1 in. (25 mm) below the bottom of the stems
of the tees. This includes sprinklers located between the stems. /[See
Figure A.8.6.4.1.2(5).]/
//
I am getting caught up in semantics with the wording. Would a
concrete beam be interpreted the same as a concrete tee?
Am I allowed to install the deflectors above one-inch below the bottom
of the beam in accordance with Table 8.6.5.1.2 as I would be if they
were concrete tees, or will pocket protection be required?
Sincerely;
Jackie "JW" Ward; SET
1-405-240-7076
jw...@firetrol.net <mailto:jw...@firetrol.net>
NICET IV Cert. No. 104187
Victaulic Vortex Integrator
Firetrol Protection Systems
108 NW 132nd Street; Oklahoma City, OK 73114
405-752-2330 Ext. 10230 Fax:405-752-2297
License No: AR-FSS-162, LA-F415, OK-863 & 302, TX - ECR-1751432,
ACR-1751168, SCR-G-0292
Firetrol Oklahoma City BACK
_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
To unsubscribe send an email tosprinklerforum-le...@lists.firesprinkler.org
--
This email has been checked for viruses by AVG antivirus software.
www.avg.com
_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
To unsubscribe send an email to sprinklerforum-le...@lists.firesprinkler.org