Rick’s and Steve’s comments are spot on. Give the fire department what they need/want. Do not install something that no one will ever use in an emergency condition. 

John

John August Denhardt, P.E.
Vice-President Engineering and Technical Services
American Fire Sprinkler Association 
301-343-1457

On Feb 21, 2024, at 13:30, Rick Matsuda <[email protected]> wrote:


Steve’s guidance is the best. 
When it comes to hose valves and standpipe requirements, always verify with the AHJ to find out what they want. 
Rick

On Feb 21, 2024, at 12:09 PM, Steve Leyton <[email protected]> wrote:



To Rick’s comments:

Concur, and also offer that while the standard doesn’t require a valve where there is no roof access, I am aware of numerous AHJ’s who do.   The stated intent of the rooftop connection(s) is to enable forward flow testing of the system.   However – and this goes to my mantra of many years now – it is incumbent on the designer to verify with the serving FD is they require roof connections that they may use for firefighting.   I have been made aware of several fire incidents that used roof connection hose streams  and I am also aware of fireground strategies that encompass these connections.  

 

The foregoing is my opinion only and does not represent NFPA or the NFPA 14 Technical Committee, nor intended to serve as an interpretation of the standard.

 

Steve L.

 

 

 

From: Rick Matsuda <[email protected]>
Sent: Wednesday, February 21, 2024 9:51 AM
To: Discussion list on issues relating to automatic fire sprinklers <[email protected]>
Subject: [Sprinklerforum] Re: NFPA 14 2019 Hose Connection on the Roof

 

This is my opinion only from what I remember after being retired for ten years. 

 

The requirement for installing a hose valve is driven by the stairway requirements found in the building code which requires at least one stairway providing access to the roof. 

 

If the stairway extends to the roof, then a hose valve is required at the top landing or on the roof. 

 

If there is no roof access from the stairway, then no hose valve is required. 

 

The fire service will use the hose valve where they have safe access from the stairway but they will not walk across the roof dragging fire hose to hook up to a hose valve located where no safe access was provided. 

Rick Matsuda 



On Feb 21, 2024, at 10:47 AM, Fpdcdesign <[email protected]> wrote:



There are people here with more experience than I,  but if one outlet goes to the roof, the requirement is met. 

 




On Feb 21, 2024 at 11:34 AM, <Joe Burtell [MT-BILL]> wrote:

If I have 3 stair towers and the middle on has access to the roof and I provide a connection as required by 7.3.2.7* “Hose connections shall be provided at the highest landing of stairways with stairway access to a roof”, do the other (2) not have to go to the roof because of 7.3.2.9.2 “The hose connection required by 7.3.2.9 shall not be required where at least one hose connection in accordance with 7.3.2.7 is provided in the building”.

 

<image001.jpg>

Joe

 

Burtell

Fire Sprinkler Manager

D

C

 

 

406-204-4653

406-861-4507

3004 1st Ave South

Billings

MT

 59101

Office: 

406‑652‑7697

www.summitfiresecurity.com

This information transmitted, including attachments, is intended only for the person(s) or entity to which it is addressed and may contain confidential and/or privileged material. Any review, retransmission, dissemination or other use of, or taking of any action in reliance upon this information by persons or entities other than the intended recipient is prohibited. If you received this in error, please contact the sender and destroy any copies of this information.

_________________________________________________________ SprinklerForum mailing list: https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org To unsubscribe send an email to [email protected]

<image001.jpg>

_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
To unsubscribe send an email to [email protected]


_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
To unsubscribe send an email to [email protected]

_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
To unsubscribe send an email to [email protected]
_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
To unsubscribe send an email to [email protected]

Reply via email to