I had some difficulty in commissioning an 8” ClaVal we installed on a 1500
gpm pump in Cranston a few years ago.  We took out the inside test header
and installed the SCV in it’s place an piped the suction line in ¼” soft
copper.  Joe from ClaVal had retired (too bad) but we managed to get a hold
of a knowledgeable outside tech who helped us out.  Seemed the ‘preferred’
location was between the discharge and pump check (not after) and the
sensing line be ½” right from the suction gauge tap (1/4”) to the operator
inlet (1/8”).  Once we changed that, it worked perfectly.  Happy birthday
GLC.

Go Red Sox.

 

From: Merle Hittle <mhit...@txfs.us> 
Sent: Friday, April 12, 2024 2:13 PM
To: Discussion list on issues relating to automatic fire sprinklers
<sprinklerforum@lists.firesprinkler.org>
Subject: [Sprinklerforum] Re: Suction Control Valve

 

It is required to be an OS&Y and located between the suction flange and the
fire pump bypass.  No preference on manufacturer other than complying with
the specifications.

 

Merle

 

From: rimrock.design.servi...@gmail.com
<mailto:rimrock.design.servi...@gmail.com>
<rimrock.design.servi...@gmail.com
<mailto:rimrock.design.servi...@gmail.com> > 
Sent: Friday, April 12, 2024 11:11 AM
To: 'Discussion list on issues relating to automatic fire sprinklers'
<sprinklerforum@lists.firesprinkler.org
<mailto:sprinklerforum@lists.firesprinkler.org> >
Subject: [Sprinklerforum] Suction Control Valve

 

I have to put a suction control valve on a fire pump for the first time. I’m
assuming it goes on the suction side of the pump. Does it go before or after
the RPZ backflow? Anyone have any preferences as to brand or model; this one
is an 8”. First time in 45 years of doing this.

 

Richard L. Mote CET

Rimrock Design Services, LLC

Middleburg, PA 17842

Mobile 570-541-2685

EMAIL rimrock.design.servi...@gmail.com
<mailto:rimrock.design.servi...@gmail.com> 

WEB: www.rimrockdesignservicesllc.com

 

Disclaimer This email message and all attachments are for the sole use of
the intended recipient(s) and may contain confidential and privileged
information. Any unauthorized review, use, disclosure, or distribution is
prohibited. If you are not the intended recipient, please contact the sender
by reply e-mail and destroy all copies of the original message. Content
cannot be guaranteed to be secure or error-free as information could be
intercepted, corrupted, lost, destroyed, arrive late or incomplete, or
contain viruses. The sender therefore does not accept liability for any
errors or omissions in the contents of this message, which arise as a result
of e-mail transmission. If verification is required please request a
hard-copy version. 

Disclaimer This email message and all attachments are for the sole use of
the intended recipient(s) and may contain confidential and privileged
information. Any unauthorized review, use, disclosure, or distribution is
prohibited. If you are not the intended recipient, please contact the sender
by reply e-mail and destroy all copies of the original message. Content
cannot be guaranteed to be secure or error-free as information could be
intercepted, corrupted, lost, destroyed, arrive late or incomplete, or
contain viruses. The sender therefore does not accept liability for any
errors or omissions in the contents of this message, which arise as a result
of e-mail transmission. If verification is required please request a
hard-copy version. 

_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
To unsubscribe send an email to sprinklerforum-le...@lists.firesprinkler.org

Reply via email to