Assuming only sprinkler piping is supported, the point loads at the hangers 
attached to the building structure would need to be accumulatively added for 
all pipes hanging from that location, depending on the spacing of the hangers, 
plus 250 lbs.  These cumulative loads then need be verified supportable from 
the structure per NFPA 13 (2022) Sections 17.1.2(1 & 2).   If both pipes are 
running parallel to supporting structural members, this could push you into 
trapezing a pipe that would normally not need trapeze.  Coordination with the 
building structure/structural engineer on where/how to hang the pipe is always 
recommended.

If you are supporting other non-system components, then you are in Section 
17.1.4 shared support territory and the 5x plus 250 lbs requirement that 
entails.

Either way, ATR diameter needs to be sufficient both for the pipe it is 
hanging, and for the cumulative sizes it is supporting which may be larger than 
the minimum required.  You may find yourself having issues with rod nut sizes 
in rings if trying to mix and match sizing from typical ring offerings.

Irregardless, detailed calculations may be required by the AHJ to prove these 
point loads can be supported and that assembly component load limits from 
bottom ring to the structural attachment, are not exceeded per NFPA 13 (2022) 
Section 17.1.2(5).

If the pipes are perpendicular to each other, it is possible you may encounter 
a situation where the upper pipe is a trapeze member for the lower pipe.  In 
this case, the trapeze requirements of Section 17.3 would apply, as would the 
considerations indicated above regarding building structural load points.

You may ultimately need a structural engineer to sign off on the detail...if 
determined necessary by the AHJ.

Hope this helps,

Ryan L. Hinson, PE*, SET**  \  Burns & McDonnell
Associate Fire Protection Engineer \ Upper Midwest Region
O 612-900-3755 \  M 763-688-4045 \  F 952-229-2923
rhin...@burnsmcd.com<mailto:rhin...@burnsmcd.com>  \  
burnsmcd.com<http://www.burnsmcd.com/>
8201 Norman Center Drive, Suite 500  \  Bloomington, MN 55437
*Registered in: AK, LA, MD, MN, PA, TX, & UT
**NICET IV - Water-Based Systems Layout

From: Brian Harris <bhar...@bvssystemsinc.com>
Sent: Tuesday, July 23, 2024 1:19 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: [Sprinklerforum] Ring to Ring Trapeze

Any thoughts on "ring to ring" instead of using Unistrut? Meaning, hanging 
lower smaller pipe from larger pipe at the deck.

Thank you,

Brian Harris, CET
BVS Systems Inc.
bvssystemsinc.com<http://bvssystemsinc.com/>
Phone: 704.896.9989
Fax: 704.896.1935

_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
To unsubscribe send an email to sprinklerforum-le...@lists.firesprinkler.org

Reply via email to