Several jurisdictions have amendments that I think are very good at
addressing this. Here is one example:

Definition: Car Stacker – A manual, or automatic, rack storage system
designed to park cars vertically
and/or horizontally such that the vehicles are in close proximity to one
another and pose an additional
hazard due to fire spread.
Design Density : Parking areas inside buildings or under attached canopies
equipped with car stackers
shall be protected by an automatic fire sprinkler system designed to a
density of Extra Hazard Group 2.
Standard coverage sidewall sprinklers, listed for Ordinary Hazard shall be
provided under each parking
level, including the bottom level if the car stacker uses a basement or pit
area. The maximum coverage
of a sidewall sprinkler is 80 sq. ft. and the use of extended coverage
sidewall heads for protection is
prohibited.
Design Area:The area of application shall be 2,500 sq. ft..
Exception: The area of application may be reduced, but never less than
1,500 sq. ft. if:
a. One-hour rated walls are provided between the stacker parking area and
other standards
parking stalls or storage areas;
b. The car stacker system is divided into maximum 1,500 sq. ft. floor areas
by one-hour fire
barriers
NOTE: For hydraulic calculations, flow from all fire sprinklers, upright,
pendant and sidewall sprinkler
heads, at all levels, located in the area of application, shall be included
in the hydraulic calculations.



Craig D. Hanson, CFPS
Fire Division Manager
West Coast Code Consultants, Inc. (WC³)
Meridian Satellite Office
*C:* 253.225.9977 | *E:* [email protected] | www.WC-3.com
<https://www.wc-3.com/>
*Teaming With Your Community to Make a Difference*


On Wed, Oct 9, 2024 at 4:53 PM Travis Mack <[email protected]> wrote:

> 2 high is in NFPA 13. EH2. 3 high is outside the scope of NFPA 13 last
> time I checked. You will need an engineering analysis for it.
>
> Travis Mack, SET
>
> *M.E.P.CAD* |
>
> 181 N. Arroyo Grande Blvd. #105 I Henderson, NV 89074
>
> www.mepcad.com | *m: 480.547.9348*
>
>
>
> *AutoSPRINK  |  AutoSPRINK FAB  |  AutoSPRINK RVT  |  AlarmCAD*
>
>
>
> Book appointment time in my calendar
>
> https://calendly.com/t_mack_mepcad
>
> ------------------------------
> *From:* James Crawford <[email protected]>
> *Sent:* Wednesday, October 9, 2024 3:15:24 PM
> *To:* [email protected] <
> [email protected]>
> *Subject:* [Sprinklerforum] Car Stacking
>
>
> I know this has been discussed but I cannot seem to find information on
> car stacking storage.
>
>
>
> Looking for protection schemes for car storage units, 2 high and 3 high.
>
>
>
> Thank You
>
>
>
> James Crawford
>
> Phaser Fire Protection Ltd.
>
> Phone 604-888-0318
>
> Cel: 604-790-0938
>
> Email [email protected]
>
> Web: www.phaserfire.ca
>
>
>
> _________________________________________________________
> SprinklerForum mailing list:
> https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
> To unsubscribe send an email to
> [email protected]
_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
To unsubscribe send an email to [email protected]

Reply via email to